I have installed a new LiFepO4 battery (24V, 200Ah) in a motorhome (expedition vehicle) that already had a LiFepO4 battery before.Current battery status: SOC=94%, 26.66 volts.
I am using a Multiplus 24|3000|70-16|230/240V
The Multiplus charger continues to work without any problems.
However, now when the Multiplus is powered on (exclusively from the LiFePO4) the inverter no longer works correctly:
It switches on and then switches off again after approx. 2 seconds, then switches on again briefly for 2 seconds and switches off again, etc, etc…
No error messages are shown on the LEDs.
My inverter settings
3.1. PowerAssist . . . . . . . . . . . . . . . unchecked
3.2. Inverter output . . . . . . . . . . . . . 230 V
3.3. Ground relay. . . . . . . . . . . . . . . checked
3.4. Inverter DC shut-down voltage . 24.20 V
3.5. Inverter DC restart voltage . . . . 25.50 V
3.6. Low DC alarm level . . . . . . . . . . .25.50 V
3.7. Do not restart after short-circuit . . . . unchecked
3.8. Enable AES . . . . . . . . . . . . . . . . checked
3.9. Load for starting AES mode . . .69 W
3.10. Offset for ending AES mode . .30 W
3.11. AES type . . . . . . . . . . . . . . . . search mode
Any idea what to do/change to get the inverter working properly again?
We need more info. What is the load at that moment? Does the voltage on the MP’s terminals change during the flipping when measuring with a multimeter? Have you charged the battery first and synchronized the smart shunt? Smartshunts remember the SOC incrementally by currents so that 94% could be the old value from the old battery.
Basically, the big inverter capacitors are charged before normal operation. Some batteries can do that automatically, others (most?) can’t. There are pre-charge devices on the market. Or you can do it more manually. Or use the MPPT to pre-charge. Others use AC but that is not supported.
DC shut-down at 23.5V is 98% usable capacity vs 99% at 22.0V. You are correct, it’s almost exactly the same.
However, if your battery empties and you try to charge it up using another one in parallel, a restart voltage of 25.5V (as per your setting) will probably make you wait for far too long, since there are 24V nominal LFP battery packs that get their voltage over 25.5V at over 80% charged. So yes, it does make sense to adjust cut-off and restart voltages as low as possible on LFPs.
Unfortunately, every LFP battery out there has indeed different values. Additionally, FLP voltage tends to be lower while discharging and higher while charging, which makes the whole thing even more complicated. Super low DC disconnect and DC restart values are my personal preference for the solar parks I do O&M for, since these backup systems need to be as quick as possible when it comes to getting them back online, after a long-duration power failure.