Multiplus II GX with external current sensor – delayed inverter reaction after AC input restore (ESS: Optimized without BatteryLife) until VE.Bus reset is performed
Issue description:
An external current sensor is connected to the Multiplus II GX 48/3000. Please disregard the battery voltage, as an LTO battery is used (Absorption voltage: 61 V, Float voltage: 58.4 V). The system is being tested with a load connected between the current sensor and the inverter input. ESS is configured in the mode: Optimized without BatteryLife. Initially, everything works as expected. A video was recorded to demonstrate the behavior.
Key moments in the video:
0:35 – A resistive load (heater) is turned on; the system initially responds correctly.
0:50 – The AC input breaker of the inverter is switched off. The load remains connected because the main grid was not interrupted.
1:00 – The AC input breaker is switched back on.
2:15 – The system still detects active load, but the battery is not discharging.
3:05 – Grid load information appears on the dashboard, although the load has been active the entire time between the current sensor and the inverter input. At this point, the inverter very slowly starts compensating for the heater’s consumption: grid power draw gradually decreases, and battery discharge increases, but with noticeable delay.
5:02 – The heater is turned off, but the system response is still slow. It continues feeding energy into the grid, and this export stops only 2 minutes and 25 seconds later.
7:30 – Grid feed-in finally stops.
7:40 – The heater is switched on again. Once again, the inverter’s reaction to the load change is very slow.
8:40 – Even after a full minute, the system still does not fully compensate the load.
8:50 – A “VE.Bus reset” is executed via the Remote Console.
10:09 – The system starts working correctly again, reacting promptly.
11:15 – My wife turned on a hot water tap, activating the flow-through water heater. While this nearly disrupted the experiment, the inverter still reacted quickly and correctly.
Core issue summary:
After switching the AC input breaker off and then back on, the system enters a state where its reaction to load changes becomes abnormally slow. The inverter does not compensate the load from the battery properly until a manual “VE.Bus reset” is performed.
Firmware version used:
Device: MultiPlus-II 48/3000/35-32
Serial number: HQ23202хххх
Firmware (GX): v3.55
VE.Bus firmware: v556
Firmware status: Up to date (20.04.2025)