I got 2 BasenGreen 16kW battery sets. Their BMS can be put in parallel one as a master and the other as the follower. However, I would like to connect the two of them independently, one on CAN bus 1 and the other on CAN bus 2.
From their own blog and information, they are designed to work with rs485 between them selves and one can connection to the Victron system, like pretty much every other battery system.
Don’t think there is any harm in trying, although what will you will be achieving? The addressing system is designed for mater slave, you can’t have two masters.
Just for troubleshooting… The batteries are new and they are unbalanced. When you have them together VRM will tell you about the V max and V min of the “set”, in this case the 2 batteries. In this way you can’t see the balance evolution by battery set. But I agree, once balanced, there is no reason to keep them separate.
I got a problem… When they are very close to 100% SOC, balancing starts. If just one cell (over 32 of them) get at 100% the BMS sends a 100% SOC to Multiplus that, in turn, move into floating. So they never get really balanced. Any suggestion on how to overcome this?
The system is in charge only mode on ESS, but on VRM it shows as “Float”. I guess (notice “guess”) it will not provide voltage as we have in Bulk so the batteries will not go up to its charge limit. It is on 99% SOC and not receiving any current…
You can’t override base programming in node red.
If you want to then set them both to the same and then use node red to lower the CVL in DVCC.
Again though to what end? Do the batteries you have have an app? Check their balance there if they are not reporting it to the vrm.
The batteries will never get over 3.4V and balanced even if I set ESS to “Keep batteries charged”. As you can see, the voltage is 54.29V. This is the float voltage set on Multiplus. I would like Multiplus to push the charge up to 3.65V on the cell that is the maximum limit of a LifePo4. However, it enters in “Float” and, unless I discharge the batteries, will not get off of this state.
Thank you for your help! If you get any suggestion just let me know, considering DVCC is disabled.
The 56.8v is 3.55v. it is sufficient for balancing. 3.65v is not safe if the balance system is not good in the bms as there will be overshoot.
If you do decide to do that don’t hold it there. Watch the CHG mos they will likely disengage