Hello everyone. I have been dealing the the situation below:
System Components:
-
Inverter/Charger: MultiPlus-II 24/3000/70
-
Solar Charge Controller: SmartSolar MPPT VE.Can 150/85
-
Battery Bank: Lead-acid (configured per manufacturer specs)
Shared Charge Settings:
-
Absorption Voltage: 31.2V
-
Float Voltage: 27.2V
-
Equalization Voltage: 32.4V
The Issue: I have noticed a significant discrepancy in how these two devices transition between charging stages. Despite having identical settings:
-
The MultiPlus-II triggers Absorption mode below the 31.2V target.
-
The SmartSolar MPPT triggers Absorption at 31.7V (0.5V higher than the setpoint).
Resulting Conflict: When the generator is running during sunny periods, if the MPPT is already in the Absorption stage, the MultiPlus-II stops charging entirely because it “sees” a battery voltage higher than its own programmed Absorption limit. Effectively, the MPPT “pushes” the voltage higher than the MultiPlus-II is comfortable with, causing the inverter/charger to remain idle.
Questions:
-
Why is the MPPT exceeding the programmed 31.2V setpoint to reach 31.7V before entering Absorption? At the Absorption state the voltage stays at 31,7V.
-
Is this a calibration issue, or is it related to voltage drop compensation?
-
How can I synchronize these two devices so they work together harmoniously when the generator is active?