Hello everyone!
I have a medium sized multiplus setup, for a smaller farm. Consisting of 3xMultiplus 15000, and 8x17kwh LiFePo4 batteries. As far as solar goes, we are talking about a huawei sun2000 50ktl, so a 50kw solar inverter. Currently the huawei is connected straight to grid, but i want to connect it to the ac out side. Huawei is prepared for frequency derating.
My question is, how strict is the 1:1 rule, and what could go wrong by crossing this limit? The huawei can be limited to 45kw max production, but is this going to be necessary? Is the 1:1rule that strict? I do have a 22kw smart controlled boiler heater and 10 000L boiler set up for export, that comes on as soon as i start exporting, and its a modulated setup, not just an on/off switch.
The multi 15k is supposed to be 15 000va, but the charger is 200A max. At 51.2v that would mean 30720W. I presume, the excess over 30kw, is going to be exported. Now since i have my siemens boiler setup, on the ac out of the multi, as soon as i start exporting(go over 30kw solar) my boiler heaters kick on.
I was thinking that i should limit the huaweis solar production to 45kwp thus, not exceeding the 45kva of the three multiplus. Then i remembered, this inverter is rated at 100A max transfer capacity. So i started thinking, and realised, maybe 10% overcurrent is not going to be a problem, because of my siemens boiler system instantly catching any exported power, before it gets exported. Currently the system is running with the huawei on the grid side, and i have never seen more than 30kw of “export”, since some power is always consumed.
If in case my batteries go full, and my 10k liters boiler also gets up to temp(which i doubt, its been installed for years, and i have never seen the siemens reach max tmp) what do you think could go wrong? Some say i will get dc ripple alarm, others say nothing, will happen, others say the multiplus’s gonna go up in flames(x doubt).
What would you guys do? Limit the huawei or not?