My test scenario/problem:
in cerbo-GX:
—Settings/System setup/ESS I switch the “grid setpoint” to -14000 which brings the inverters within a few seconds to ~ 3* 3450W output and stabilizes there with +/-50W.
—in my test i also switched on consumers with a total consumption of 12500W in the house - inverters also stopped at ~ 3* 3450W and the gap (~2000W) was filled with electricity from the grid.
Some details about my system:
-2* 48V 16kwh battery packs supporting 400A and configured for 300A max. discharge. (config in JK-BMS, serialbattery-driver, aggregateBatteries; aggregateBatteries provides 300A discharge current to the cerboGX in the parameters)
-1* Lynx shunt between both batteries and rest of the system
-3* muliplus-II 5000 in a 3-phase configuration
-DC wiring is 50mm² between busbar and MP and 95mm² between batteries and busbar, busbar is 1000A Victron distributors and power-ins.
-MPPTs are not really relevant, the problem persists also when PV provides (partially) the power to feed the inverters directly.
-AC cabling is 16mm² to each multiplus (=>4x16mm²) connected directly to connection house <=> grid.
-Fuses for the AC between MP-II and grid are 32A circuit breakers (per phase) and 50A (melting) fuses (per phase) for the whole house.
-MP-IIs are connected to AC-IN, AC-OUTs are currently not used.
-MP-IIs are controlled via Cerbo via the EM540, which is placed first, when cables come into the house from the grid (after the 50A fuses).
-Software/firmware: I am using latest/stable for all devices, so e.g. v3.60 on Cerbo.
-System is running for 3 months, Victron equipment bought new in 08/2024.
What I did:
-checked multiplus settings via VE Configure
-checked JK-BMS, serialbattery, aggregateBatteries for possible wrong limits
-checked CERBO-GX settings (v2):
— System Setup/ESS/Peak-shaving: “Multiphase regulation” => Total of all phases
— System Setup/ESS/Grid feed-in: “DC-coupled PV - feed in access” => on
— System Setup/ESS/Grid feed-in: “Limit system feed-in” => off
— System Setup/ESS/Peak-shaving: “Peak-shaving” => Always
— System Setup/ESS/Peak-shaving: “Limit system AC export current” => off
— System Setup/ESS/DVCC: “DVCC” => on
— System Setup/ESS/DVCC: “Limit charge current” => off
— System Setup/ESS/DVCC: “SCS- Shared current sense” => on
— System Setup/ESS/DVCC: “SCS- status” => Disabled (external control)
— System Setup/ESS/DVCC: “Controlling BMS” => AggregateBatteries
-checked VRM portal settings:
—Dynamic ESS is enabled, but not used due to being switched off in the main dashboard
—Still all settings should be fine.
------System: “Maximum export power” is set to 15kw
------battery: “Maximum discharge power” is set to 15kw
-checked temperature above the MP-II: It goes up to max 40° (According to Victron docu the expected limit is at 45° ~3700W, so no explanation for the limit of ~3450W)
My strong assumption is that the MP-II should be capable of producing at least 3x3700W, so >11000W even at the highest measured temperature.
Also a technical issue inside the MP-II I would consider very unlikely, because the output rises more or less linear with constant speed to the 3450W.
Any ideas or tips how I could resolve the issue?