Hello,
I have an off-grid installation with:
- Victron MultiPlus-II 48/5000/70-50
- 48V battery bank (~15kWh)
- 5.5kWp PV
- TT earthing system with earth rod
For generator backup I currently use an old three-phase generator connected directly to the AC input of the MultiPlus.
I also own a Pramac EPW3000 Electric Start generator (230V single phase, AVR, 2.7kW rated output), but it has never been connected because my electrician identified it as a floating-neutral generator and was concerned about the earthing arrangement and RCD operation.
According to the Pramac manual:
“The mid-point (neutral) conductor of this equipment is not grounded.”
The manual also states that when supplying a facility in a TT network and where residual current protection is required, a 30mA residual current device must be installed and the generator frame must be connected to earth.
My questions are:
1. Is a floating-neutral generator such as the EPW3000 compatible with the AC input of a MultiPlus-II 48/5000/70-50 in an off-grid TT installation?
2. What is the recommended Victron-compliant arrangement for neutral-earth bonding when the generator is connected?
3. Should the N-PE bond be provided by the generator side, by the installation, or by a dedicated switching arrangement?
4. Is there any specific Victron documentation or Wiring Unlimited section that covers this exact scenario?
At the moment the generator has never been tested with the MultiPlus, so I don’t know whether the issue is a real incompatibility or simply an installation/earthing concern. The electrician, seeing that it had floating-neutral, decided to use the old generator (Where neutral and earth were connected). But It has less power (in a single phase), worse frequency control, and basically is worse in all senses, so I am still trying to use the newer one (Which we bought for our previous inverter, which used an external charger for the 24V batteries)
Thanks in advance.
P.S.: I have seen some post about this, like Inverter generator on Multiplus AC IN - DIY - Victron Community ot Generator hook up to Multiplus 2 10kva, floating neutral question - DIY - Victron Community but not sure about what is usually prefered here, so I opted for opening a new thread.