Multiple Battery Info on DVCC

How much battery info should be displayed on the Dashboard or Remote Console. So far, mine only shows quantity of batteries and total capacity. The other info seems to be front one battery or an average. I am using 2 each SOK 12.8v314AH batteries which are daisy chained to the Cerbo VE. Can Port 1using can-bus BMS-LV, 500kbit/sec setting.

Side question: what are the 2 ::2, 1 ::4, etc, designations below?

These are all the devices in the system.

First number is the battery and the second one is the cell number inside that battery. This data is forwarded by the BMS.

You are seeing what is shown, data is limited by the bms and BMS CAN spec.

is this really safe?

i´m glad my system is monitored down to each single cell

It looks correct for two batteries in parallel.

It is, there is no need for the GX to track every BMS metric, it would make the CAN spec and comms busier. Ultimately, that is what BMS tools are for.
The GX is showing a window into the BMS and the relevant metric is understanding if a significant delta is developing which is a guide to go dig a bit deeper. Ultimately the BMS will start generating alarms and taking action if a real problem exists. It will do that irrespective of how much information it is or isn’t sending. Temp and voltage min/max have been sufficient for all the commercial batteries, with VRM charting the various cell id’s as the state moves during charge/discharge. Too much information can also be counter-productive. Having diagnosed a few bad cells by now, can’t say I have regretted not seeing more cell stats. Battery manufacturer support generally can figure things out with this view as well, though, they do sometimes want data straight from the BMS if they need a broader view, something that the GX would never accommodate.

It’s not rocket science :wink:

Thank you. So it appears that data is shown and can be shown for both batteries.

Odd that the high and low temps are for Battery 1

KR, That was the info I was expecting. I suppose SOK just supplies the bare minimum.

KR, What battery do you use?

It is a self made battery - 2 banks, each 16 x EVE LFK-280, each supervised by a Daly BMS

The BMS (the Hardware piece) only could send alarms or switch of charging / discharging

I have problems with my older Battery bank, when almost full, Cell Voltages differ

As i see each Cell voltage, i could set a max cell voltage, if that is reached charging current is reduced to give the battery time to balance

This is only possible if something tells the Victron System to reduce charging current

In my Case this is done trough Daly-BMS in conjunction with DBUS-serialbattery-software

I don´t know, but could imagine that other batteries like Pylontech do the same internally, tell Victron System to reduce current

SOK advertises them as Victron-compatible, but a battery that sends only a fixed max charge current / voltage, regardless of cell voltages, doesnt make much sense

That could be due to cell resistance or wiring.

For example. I previously had a Victron switch installed close to the battery plus terminal. And it ran hotter (32°C) during charge sessions than after moving it. The heat generated by the resistance of the Victron switch, had a significant impact on the temperature. Now it’s only a matter of a few degrees higher than the other cells.

Many of the so called Victron compatible batteries (read: BMS) can be monitored with the help of NodeRED. I read the maximum temperature and voltage, and when that seemingly gets out of control, I either lower or stop charging altogether. Based on the values.

Similar DIY setup here, and one thing I’d add: with two banks, it’s worth checking in the device list that both batteries show up as separate services so DVCC aggregates them properly, and that the charge current limit from the weaker bank is the one driving the whole system. If you’re also using dynamic pricing or DESS, watch how the BMS-requested current limit interacts with the scheduled charging, since a hard limit can make the charge schedule lag behind. Backing off the current when the max cell voltage is reached is exactly the right approach to give the balancer time.