I currently have three Multi RS units installed, each with MPPT trackers. Starting next year we won’t receive a cent anymore for the solar power we feed back into the grid. My idea is to keep grid export at 0, but it looks like the Multi RS doesn’t (yet) have this function? Or am I missing something?
Yes you can, Multi rs manual page 21(Dutch language)
Thank you. “Feed‑in allowed” is the option I was looking for.
Is it not possible to change this setting on the Cerbo as well, or can it only be adjusted through the VictronConnect app?
I have also the Multi RS 6000, running well for 5 months (except some ocasional problem with bms/ charging) every change I do is in the Victron Connect App (or on the Victron Touchscreen), on every component itself, the Cerbo looks more like simple connection box.
The control of Victron gear is very over-complicated.. it seems impossible to get get the full potential out of the Victron equipment.