Hi,
I have a system with 3 MPPT´s , two 150/35 connected via VE.Direct to a CerboGX and one 250/100 connected via VE.Can to the CerboGX, this works perfect
The problem is that when I connect another MPPT 250/85 via VECan it don´t synchroniz with the others. It consider it self to be “standalone”
All firmware is updated.
250/100 status: Group Master. State: Ext.control
150/35 status: Slave. State: Ext.control
150/35 status: Slave. State: Ext.control
250/85 status: Standalone. State: Absorbtion
Yes, I have a CerboGX and DVCC is enabled.
There is synchronization between the two 150/35 (VE.Direct) and the 250/100 (VE.Can)
But the newly installed 250/85 (VE.Can) vill not synchronize with the old ones.
Hi
Well, I got it “sort of” sorted
I connected the MPPT via VE.Direct and it started to behave as “slave” and syncronized charging with the others.
Not the way I wanted but it works for now.
Dont have any ideas what could be the problem with the VE.Can
Strange, bad cable, missing or faulty terminator?
Ok but the VE.Can on the MPPT might be faulty.
Worth a look 6. Troubleshooting Guide - MPPT
Good luck.
Dave.
I have two 150/35s connected via ve.direct to a cerbo-s. Then I have a 250/100 and 450/100 connected via ve.can.
Only the two ve.can connected sccs show an entry for “Network total power” in VC, the ve.direct connected sccs arent included. I asume this is normal as the ve.direct and ve.cans arent combined? They all do show up in vrm etc.