Mppt and BMS 12/200

good morning everyone, I installed a 200Ah Victron lifepo4 battery and a 12/200 smart bms on my boat. I also have 3 Victron solar regulators that I wanted to connect to the engine battery so as to use the 12/200 bms to disconnect the charging of the lifepo4 battery when the voltage reaches the threshold preset by me. Yesterday I went out for the first time, I started the engine and after a bit of navigation I noticed that when the set threshold value was reached, the bms disconnected the charging of the lifepo4 and immediately the voltage of the engine battery began to rise up to 16v. I disconnected the charging of the 3 Mppt and the voltage dropped. In practice it is as if the Victron MPPT algorithm did not know this eventuality, as if it sensed a sudden drop in the current request as if it were a resistance and dangerously increases the voltage of the engine battery to which the regulators are connected. I hope that the Victron technicians will be able to solve it, in the meantime either I install a battery protect for the solar panels or I will have to turn off the MPPTs when sailing under engine power

Would you please post the MPPTs settings, this is not a normal effect.

Do you have a standard lead battery connected to the alternator?


with mppt regulators deactivated, when the bms disconnects, the engine battery still goes up to 14.8v, but it’s already better this way. However, I’m afraid of this continuous disconnection and connection of the bms, I hope nothing happens

Could it be the presence of a 200A fuse that I put on the alternator-engine battery line?

I finally unplugged the solar regulators and everything started working properly again.

Do you have a BMV/SmartShunt and GX device with DVCC activated?

yes, both, but what would be dvcc?
Edit dvcc not actived

Did you configure a VE.Smart network between the devices?

Yes, with victron app

Which devices did you add to the smart network?
Maybe add a schematic of your system.

You might have to remove the MPPTs or the shunt from the network.
If the MPPTs get a voltage transmitted from the shunt they try to increase the that voltage by increasing there output voltage.

I have 3 mppt regulators, a ip43 phoenix charger and the smart shunt. The voltages are the same in all the measurements of the individual devices, so no voltage drops. now I try to activate the dvcc so we’ll see what happens, but I’ll be back on the boat in a week, I’ll update you. thanks for the moment

No, that will result in the same problem if the MPPTs are not connected to the same battery as the shunt.
If you have connected the MPPTs to the starter battery they have to run in stand-alone.

ok ok. So what can cause this problem?
And finally I did not understand if you wanted the mppt on the system+ port of the bms smart 12/200, would I have the bms protection that will disconnect the charge when the voltage reaches the maximum? Because from the bms 12/200 there is no possibility of regulating except the maximum voltage from the alternator port. I am quite confused on how to connect these mppt regulators

I connected the solar regulators on system+ of the bms 12/200 and now the system+ port reaches 16v with the solar regulators active and the engine running, despite the bms disconnecting the alternator. The voltage of the system+ port varies continuously, from 13.3v to 14.6v if I connect only one solar regulator, if I activate 2, instead it also reaches 16v. With the engine off, everything stabilizes and no problem. I’m going crazy

The manual shows how to connect it:

Disable the Smart Network or at last remove the shunt from the network.

The shunt is sending a voltage that the MPPT wants to reach.
If the BMS blocks the current into the battery it causes the MPPT to increase it’s output voltage to raise the voltage transmitted by the shunt → the voltage at the shunt isn’t rising → MPPT increases it’s output more and so on…

but this way I should connect the solar regulators with the vedirect port to the charge disconnect port and I would take advantage of seeing the solar regulators on the Cerbo GX

[anyway now I have unfrozen the smart shunt from the network, later I will try to see what happens