I am in the USA. I configured the MP-II for 240VAC, 60 HZ. It is connected to a Victron AT-100 autotransformer. The Critical Loads sub-panel does not have the neutral bonded to the ground. The Main Service Panel does have the neutral bonded to the ground.
The transformer output is wired split-phase to a breaker panel with only 120VAC loads connected. I disabled the Internal Ground Relay in the MP-II settings. The External Ground Relay output is wired to the AT-100 Earth Relay input.
I am using a Klein CL-800 clamp on current meter for all voltage & current measurements.
When the inverter is powered via battery, the AT-100 split-phase output is perfect. I get ~120VAC on each hot leg. With 2.4 amps of current on one hot leg, and 1.6 amps of current on the other hot leg, I was measuring roughly 1 amp of current on the neutral leg.
When I power on the mains to the MP-II, the current on the hot legs of the AT-100 remains the same. However, the neutral current immediately jumps to 15 amps.
There are no error messages or fault conditions on the MP-II. The Cerbo / GX-Touch 50 report no error conditions.
Why is there so much current on the neutral leg of the AT-100 when the MP-II is powered by the mains?