Good afternoon, I currently have a grid tied ac inverter with a Multiplus ii 48/3000, smart shunt 500, Cerbo mk2, and 2 banks of 4 x TNE12-125 agm batteries ( 250Ah) ET112 energy meter as grid meter and also 1 ET112 for PV production. The system has been running for in excess of 4 years. Batteries approx 20 months old.
Just recently, as the sunshine has been getting less I have noticed a couple of issues, i.e. that the system stops inverting when the batteries are showing anything from 77% to 60% soc. Alarm indications of low battery from either the Multiplus or smart shunt, yet no indication of #1 or #2 ESS battery codes. Very frequently the Multiplus will revert to sustain Sustain ( as now with 64.2 % showing with a voltage of 49.2 v, current- 0.2)
The question is : How do I get the ESS battery error codes back ? and why does it does it fail to invert and reverts to Sustain rather than discharge the batteries to their nominated 45 or 50%
I have checked and re checked the manuals and settings yet cannot find nothing obvious. If I split the bank and run just one set of 4 batteries ( 125 Ah) I get ESS #1 and #2 messages when the voltages drop and SOC falls on either bank (having obviously amending the battery bank size in ESS on the Multiplus and shunt ).
Thank you in anticipation
21225.TXT (2.3 KB)