I recently installed a MultiPlus-II 48V 3kVA unit to replace my trusty Sun Grid-Tie inverters :). Before this upgrade, I was running multiple Sun GT inverters on both legs of my system.
My setup:
48V battery system
Victron Charge Controllers
Cerbo GX
Victron Shunt
Remaining Sun GT inverters still active on the other leg
CT sensor installed for the new Multi.
Multi connected to the grid via a 30A breaker on the AC-IN port
My goal:
I’m located in the U.S. and cannot export to the grid. I want to use the ESS function to import just 10–20W (even with full battery) and self-consume as much as possible from solar and battery. I fully expect to import power when needed, as I’ll never produce enough solar to be off-grid.
Issue:
The Multi is only inverting around 4W, and the system shows the grid as “Disconnected” in the GX system. My battery has plenty of capacity, so I expected it to be inverting more. I’ve set the Multi to “Inverter Only” mode. I’ve read a lot of documentation and forum posts, but I still can’t figure out what I’m missing.
In the GX screenshot, the DC Loads represent the Sun GT inverters operating on the other leg.
Hello Nick. I’m attaching all the settings pages from the VEConfigure, except the advanced page which unchecked. The ESS pages are mostly default, just changed the battery type to LifePo4.
I tried a couple of different CTs, which are not Victron but now I’m wondering if Victron CTs are very special… Those CTs that I used are 100a, 50ma, same rating as Victron’s.
Ok, I think I found my problem, I changed the Multi setting from “Inverting” to “on” now, it’s properly displaying and inverting battery power to AC. I thought it should be “inverting” since, i don’t want to charge my batteries from the AC.
Another thing, even though I set the grid point 40W, it fluctuates to export a few watts from time to time, I might need to set it higher. Do i need to worry about the code ESS #6?
I have ESS#6 most of the time. It just means I have set the charge current to 0. I use DVCC to set it 0 I dont know where you could have it set to 0. Maybe you have overruled in remote?