Hello,
I have my solar system running for just over a year now, but at first it was temporarily installed with pair of MPPT 250/100 due to unavailability of MPPT RS 450/200 unit that I ordered.
Background:
My installation consist of 16 panels - Canadian Solar CS6W-555MS, with specs as follows:
Pmax: 555W
Vmp: 41.9V
Imp: 13.25A
Voc: 49.8V
Isc: 14.05V
Max System Voltage: 1500V
Max Series Fuse Rating: 25A
MPPT RS is connected to 3x Pylontech US3000C, providing c. 10.5kWh of storage.
The panels are currently split into 2 arrays, East and West facing. I assume due to the use of MPPT 250/100 at the start, each array was configured as 2 paralleled strings of 4 panels to keep the voltage under 250V. This setup worked well.
Problem:
When eventually the pair of MPPT 250/100 were replaced with my shiny MPPT RS 450/200 without modifying the arrays layout (simply using 2 of 4 trackers of MPPT), I noticed that on sunny day the MPPT trackers max out on 16A per tracker, which matches the limitation listed in the data sheet.
Search for solution:
I am looking for the solution as with the sun climbing higher every day, I see the system maxing out regularly, which obviously is a waste of solar power.
I am looking for the best solution, and as far as I can see there are only two solutions available (if not just one):
-
Break the paralleling and use all 4 trackers to run 4 arrays of 4 panels in series. This sounds simple and logical at first but:
- requires doubling up on the array protection and isolation equipment on the roof, which done right is costly
- requires another two pairs of solar cable runs back to the MPPT. It’s only c. 25m run, but an awkward job requiring climbing into not very nice places
- it limits any future capacity expansion to the existing area only as I’d be using all 4 trackers, so connecting further panels in series would be my only option
-
Reconfigure each array as string of 8 panels in series, which would be much simpler, but after running the idea past Victron’s Click & Design I was told that this won’t work, it throws the following errors:
- Increase the battery float voltage or reduce the voltage on tracker 1.
- Increase the battery float voltage or reduce the voltage on tracker 2.
Configuration validates after removing 1 panel from each array (ie. 7 panels per tracker). I assume the error is related to this limitation of MPPT RS:
MPPT operating voltage range is constrained by battery voltage - PV VOC should not exceed 8 x battery float voltage. For example, a 52.8 V float voltage results in a maximum PV VOC of 422.4 V.
My battery float voltage is set to 51V, which as I understand is a recommended value for my batteries, but Click&Design only validates after float voltage is changed to 55V! With that in mind, something doesn’t stack up for me here as 8 x 51V (float V) must be more then 8 x 49.8V (Voc)… it doesn’t take a math genius to work that one out.
Questions:
- Am I missing something else that constrains my preferred reconfiguration?
- Am I completely nuts thinking about creating the setup so close to limits?
- What would happen if the array voltage was to exceed 8x float voltage?
- Is there anything else that I am missing that I should be aware of?
Thank you in advance for any help, recommendation or even pointing in the right direction.
Regards,
Sergiusz