Inverters see AC-In voltage and freq, but not connecting to grid
I have a Grid-tied UPS setup, using two Quattro 5k’s. It’s worked well for a few months, with occasional outages and recoveries-- very minor ones. Recently, we had our first major outage. The batteries are drained to ~2%, but the inverters aren’t reconnecting to grid!
In the status screens, it shows that it sees AC-In voltages and frequencies that look healthy
I’ve also enabled wide frequency input.
We’ve tried power cycling with the main Quattro switches, resetting the VE.Bus, and I’m at a blank… please help!
We also just noticed the second inverter’s status lights went off and the first unit is flashing status lights between Inverter On and Float–the manual doesn’t have anything listed for this…
Thanks,
Mike
Looking at the faults, there is no fault 1 being listed.
Here’s the list of faults.
  • We have had roughly weekly outages with no issues before, but never 24 hrs draining the batteries this much
  • The alarms are making me distrust the VE bus. We’ve tried resetting it a few times, sometimes with differing effects.
  • I was upset with Signature Solar for not providing cables for these connections, but I seemed to have got it to work in the past… Here’s what I understand about the VE bus:
  • There are no terminations, like on the VE Can.
  • We’re using CAT 5E cabling that we had around.
  • I have one cable from each inverter going into the VE bus ports on the GX. Of the cables I had, one of the cables is Cat 6 patch 24 awg, the other is Cat 5e 26 awg (not patch)
Do you have to use patched vs not patched Cat 5?
Other thoughts??
Thanks
@mjs333
Hi Mike
The connection on the ve bus is one inverter to the other than then one from the inverter to the GX. (I usually use the master. I don’t think it matters - never tried it anyother way.)
They use straight (also known as patch cables between the gx and the inverters.)
You are correct you don’t need a can terminator.
The system is in float with is strange if it needs a charge.
How is your system programmed?
@Ludo Grid should be good. voltage and frequency are showing all in spec.
@lxonline We tried switching the ethernet cables as you described. Sadly no improvement.
Update:
I reconfigured the units to be independent (turned off any 240V split phase loads). The master unit came back to life, is passing grid power to the loads and charging the battery!!
The second unit is faulted, but I can’t figure out in VictronConnect how to read the fault (using the PC version). We also noted the GX display wasn’t displaying the faults earlier… not sure if related.
I’m hoping maybe it wants a higher battery voltage, and it will come to life in a bit with more battery charge. But I’d really like a way to read the fault…
@mjs333
It will be in fault mode of left as previously programmed (part of a split phase set up) as it is looking for its partner.
Reset to default and see if the fault is still there. Victron connect usually has a banner on it if there is a fault.
@Ludo Understood… wouldn’t the other inverter fault if this was the issue? The other inverter has been rock solid.
@lxonline Correct, we went in and reprogrammed both inverters to be standalone using Victron Connect. It does show a fault, but we can’t see what it is!
To be clear, we disconnected the second inverter from the Cerbo GX (we tried with it connected to the GX and the other inverter disconnected… no difference–faulted either way)
A firmware update is definitely the next move.
Unless you feel you are at the point where there is a warranty claim? Work through the testing in the pre rma form.
Checked firmware versions a few days ago—all updated.
The VE Bus tools is something I’ll try to read the faults. (Sadly I’m doing this all remotely, with a friend at the house… can’t try now)
I will also check a few settings to make sure they were mirrored correctly:
  • Accept wide frequency range
  • Weak AC
  • Power assist off
  • check voltage limits
  • I could have sworn I checked if the AC ripple was triggered, but will do again
With the units independent, it lets the good unit charge the batteries, while the bad unit inverts to supply power to the loads… works okay for now. I just can’t power my 240v water pump.
Thanks for all the thoughts—any more are welcome
@Ludo, where do I find the information on why it’s not connecting? We didn’t see a fault, but this one unit is still on inverter only (the other unit working well).
  • I verified the following settings: Accept Weak AC: on; Power Assist: off; Accept Wide Frequency Range: on
  • Voltage and frequency were in-spec, and no errors
  • Here is the display from VE Configure, looking at the VE Bus. Should UMains be orange?
We did notice a few things that caught our eyes. Let me know if these rings any bells:
First, I noticed this tab… I have no idea what this stuff refers to. Thoughts?
Second, we noticed the following in the NS Protection Log. I think this refers to the battery… could be related to how we’re messing with the VE Bus connections to get the two Quattros operating independently for diagnosis… This inverter is operating without comms to the GX, battery, or shunts. My quick google seems to indicate these under voltage entries refer to the battery–which is working fine. Let me know if you all have other thoughts.
Thanks all
Thanks for the inputs… will check all connections in the morning.
Hi All,
  • Connections were all tight–no change.
  • Interestingly, when we went to tighten the connections, the grid was down… had a 6+ hr outage before we got feedback on if anything changed. But alas, we still have a fussy unit regarding accepting the grid.
We did take screenshots of all the VE Configure tabs. Again, I don’t understand the Virtual Switch, so I’d love help looking at those settings. Of note, now the frequency is also orange… the values look totally fine to me though! We’re still getting the Under-voltage log entries on the grid tab…
More screenshots:
On the final advanced tab, we are not limiting charge to prioritize other energy sources. (just didn’t want another post)
I agree.with ludo the settting are off/in conflict.
Work without VS for now. (So disable it).
It is like conditional AC connect when you program with Victron Connect. You don’t want this right now.
Establish that is does connect, charge etc.
Weak AC is good if there is a generator that will be used combined wide frequency settings
But those settings conflict with UPS.
(so choose there- one set or the other)
@lxonline for learning purposes, can you explain more behind weak AC + wide frequency vs UPS? I don’t think I’ve run across any documentation noting these conflict each other.
Update. We tried the following, in order:
  • We turned VS off
  • Turned UPS off
  • Turned wide frequency and weak AC off
  • We switched to charger only
None seemed to accept Mains.
A few things we noted along the way:
Finally, we decided to try copying the settings from the working unit to the fussy unit. No change.
Are we at a warranty claim?
Thanks
Are the errors appearing in time with the relay clicking to connect?
As you watch the green bar progresses (as it is synchronizing) then the relay click.
If the voltage is dropping at the click -h> then maybe there is another issue like a dodgy breaker or high resistance connection. (So heat shrink or tape under the lug on the ac connection - or insulation clamping in a breaker etc).
I think you are at this point after checking with a DMM as it is conecting if there is or isn’t real voltage drop. (Just imagined by the inverter :laughing:)
VE.config has a build-in help.
Menu → Help → “What is this?” → click on the item you want to learn more about
@Ludo the errors were live
@lxonline interestingly, we weren’t hearing any clicking when the bar got to the end… maybe that’s a sign of a bad relay?
Unfortunately I lost my cousin helping down at the house. We pulled on wires and tightened connections, so I don’t think it’s that. I can’t do the help without being connected to the unit. Is there any documentation that explains how those settings are in conflict?? What happens if both are active? I highly recommend something like that get added to the Quattro manual! I ran these settings by other forums, and nobody batted an eye.
Logic?
UPSs only accepts a small voltage range (and no sudden fluctuations) and is fussy about voltage and frequency.
The other two settings are telling the system not to be fussy.
Ergo - conflict.
If the relay is not clicking something is not right.
It would usually make at least three attampts before calling it quits.
I had the same problem. It turn out the contactor points were burned. I pulled it apart redid the contacts.