In a parallel system, “each unit needs to be fused individually”?

Having recently redesigned and installed a complete Victron AC/DC (12v) system including Lithium Smart batteries and using one MultiPlus II (12/3000/120-50) inverter charger, I have realized that I not only need more AC power, but I also need more charging power as well, so paralleling 2 MultiPlus II’s seems to solve that issue.

According to wiring unlimited:
"Each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to the same resistance.**
Consider using mechanically connected fuses”

On my boat, Shore Power comes in at 240 volts/50 amps to an Isolation Transformer. Power from the Isolation Transformer goes to a Balance Transformer where it is converted to 120 volts. A single 120v hot line and neutral line come from the Balance Transformer, then through a 50-amp breaker and to the inverter (the explanation is somewhat simplified). I never want more than 50 amps through this line.

So, here’s my question:
Why do I need a circuit breaker for the line “IN” on both MultiPlus II’s? Why can’t I split the line after the 50-amp breaker and go directly to each unit?

The ability to have easy isolation, and protection for the device, would be my suggestion as to why having separate circuit breakers per AC IN is a good idea.

The part in wiring unlimited I read as referring to DC fuses and wiring. I would add that the DC wiring will need to be balanced.

Hope that helps.