I’m trying to recreate an ESS, that is an all-in-one solution from a UK provider. It is Victron Kit under the hood.
Can anyone identify what victron product is being used as a grid meter here.
It is connected via RS485 to a Cerbo GX.
It has 3 phases. L1 is set to grid. L2 is PV meter
All the current sensing is done via CT clamps, and not in-line meters.
The product ID is b031
In this particular installation it is clamped on the grid meter and PV. The PV is 6kW ( ~25A) and the grid is well up to 100A which is has measured over 10kW at least. so well above 5A…
it’s a CT connection…the Clamps need to be rated for 5A internally, on the meter side…you need to deploy the correct clamps for the AC side, like 100A or 200A…