I have a multiplus II with a couple of mppts, a battery and is connected to grid. (ESS)
(Grid setpoint -20W)
All is working fine but I want to connect a micro inverter (Hoymiles) to the system on L2/L3.
Today my Victron system is connected to L1.
In a perfect world I would connect the micro inverter to L2/L3 and my Victron system would see the extra production and not get confused with a gridpoint set to -20W.
Use an “OpenDTU” to read out the Hoymiles using the properietery Nordic radio protocol.
Forwqard the values from OpenDTU via MQTT to Venus OS / Cerbo GX.
Integrate the data via “dbus-opendtu” with appropiate configuration naming which hoymiles is on which phase.
I have this running wiht 4 HMS-2000/1000 and one HH-600 on different phases. Works like charm.
If the hoymiles are connected to AC_in, they will stich of in case of grid falues.
If you connect them/some on AC_out_1 of the MP2, you need to obey the "factor 1 rule! and confifure PV assistant to increase network frequnency in case of SOC becomes 100%. Latests at 53Hz the Hoymiles will shut down, but there is a power derating curve according AR-N-4105.
Thanks.
I am thinking of connecting the Hoymiles to L2/L3 and integrate it with
In that way I will get the solar production in to my VRM.
@BjoernK Are you running your system with ESS? How are you handling the “grid set point” ?
If my house is using less power than the hoymiles produces do I sell the surplus or will my Multiplus charge the batteries?
Yes, ESS. GridSetPoint=0W.
If HMs produce more than current consumption, the MP2 load the diff into battery.
That’s exactly the purpose of an ESS.
Depending on your country, a MP2 on L1 can load from L2/L3 (net metering, like in DE).
Just a remark:
Assuming your system ist grid connected and the
Battery is full:
Sun is shining->hoymiles is producing more than you can consume.
In that scenario it is NOT possible for the victron system to hold the grid setpoint (-20W in your case).
The access power is fed into the grid.
Reason:
Due to the fixed frequency which is provided by the grid the victron system cannot increase the frequency. Therefore an AC-out connected hoymiles (any AC-coupled Inverter (Exception: may be a modbus controlled device)) does not reduce the power.
AC-in connected: there is no way to controll the micro-inverter.
REMARK to the remark:
If you use hoymiles with openDTU or ahoyDTU you can set the output power of the hoymiles and controll it that way. But further programming is needed.
Have fun
Marc