Simply put, enough power is only ever produced as required by a load. Even if the solar panel array has a 1000W potential, a 100W load will only result in a 100W (plus some possible losses) of power being produced and consumed by the load. To answer your question, no the system does not disconnect. PS - Best to think of it as 9kW of potential not realised as opposed to wrongly 9kW of power lost.
If the PV inverter is connected via the GX and supports it, then the system can tell the pv inverter to ramp down or run throttled.
For example Fronius suports control via modbus.
Not all PV inverters are fully integrated for control like that though. (Some only have basic monitoring)
Well… I am in Europe. Here you are not allowed to shift frequency when on grid and would need a lot of power to surpass the grid power capacity to shift it. So, it is not a problem on the inverter being used, Multiplus should not shift frequency while on grid.
As LX mentioned: if your PV inverter is linked to and supported by your GX device (Fronius PV inverters work very well), the GX can tell the PV inverter to produce less power, so the FeedIn limit can be achieved without frequency shifting.
Because indeed: when you are connected to the grid you can 't shift frequency.
Another remark: your PV inverter should be correctly configured to properly integrate with a GX.
From the top of my head are these the settings that need to be configured on a Fronius inverter:
Modbus config needs to be set to the “int + SF” Sunspec mode
Inverter control via Modbus needs to be enabled
Control via Modbus should have priority
Please check the ESS manual on the relevant topics.
The problem is that this is an integration of Multiplus II on a site with SolarEdge inverters that also includes a battery. It gets quite confusing when it comes to decide who does what.
I guess that the best approach is to keep the SolarEdge power meter measuring the import/export (before the Multiplus AC input) and having SolarEdge, if necessary, limiting the export. But as a side effect, the SolarEdge battery will only get charged when the Multiplus’ batteries are fully charged as it will be seen, from the SolarEdge perspective, as load.
Correct, this is also documented as needed with some models. They use sunspea as does Fronius on some models. So the possibility for some models is there.
To make it a little bit more complicated, one of the two SolarEdge has a 10kW battery. The Cerbo GX Sunspec SolarEdge data collection will only work if you set the SolarEdge modbus number to 126 but, if you do this, then the SolarEdge looses control on its own battery (LG bug?). I have posted a question if it would be possible to change the Cerbo requirement of setting up the SolarEdge to modbus address 126, but got no answer from the community (too complicated?).
By other hand, I can have the SolarEdge always set to be on what they call Alternative Power Source mode (APS) were its production can be controlled via AC frequency so, by Multuplus II. Still, it only applies when the system is off-grid as you can not modulate frequency when on grid.
When in off-grid (e.g.: the grid went down), if you do not control the production, and the batteries are full, there is no place were the power can go. As you loose the SolarEdge power meter (the grid line is “open”) then it will produce at its maximum. In this case, you need Multiplus to increase the frequency so it will reduce/stop the SolarEdge production and the SolarEdge must be in a state that adjust its production based on frequency.
I could use Multiplus II K1. However, K1 now is not a physical relay but a open collector transistor. So you need one external relay or an optocoupler. As Multiplus will always be driving the house, I think it is easier just to keep SolarEdge in APS mode.
No… SolarEdge does not provide off-grid without installing what they call “backup interface”. The backup interface is very expensive. Also, if grid goes down it takes few seconds to bring the power on back again. That is why I choose Victron Multiplus II.
In this case, Multiplus is always the AC reference. While on grid, it follows the grid; while off-grid, it generates the AC reference so the SolarEdge can keep producing. From SolarEdge I charge all the batteries. However, next week I will move one PV string out of one SolarEdge and connect it, via a Victron MPPT, to the Multiplus. This will provide starting capacity even if all batteries get totally discharged.
For those reading my posts, I guess now it will be more clear that much questions I am posting.