jabuchol
(Jason)
10 February 2026 00:38
1
Multiplus II
When linked - do you have one large battery bank and the 3 units connected to there same battery bus? Or does each Multiplus run its own battery bank?
I want to input and output 208 3 phase. Can you current limit the battery charge current when in 3 phase mode?
Many Thanks
Justin
(Justin)
10 February 2026 01:09
2
All must be on the same battery bus, with equal wiring and etc. Have a look at the parallel & 3-phase manual, and all docs/training videos linked therein: Parallel, split- and three-phase VE.Bus systems [Victron Energy]
2 Likes
Very directly though.
Yes
No
Yes the programming is very configurable and flexible.
jabuchol
(Jason)
10 February 2026 16:20
5
Thank you. Next question, can I wire the 120v out from each of the three units and get 208v? For example tie L1-L2, L2-L3, and L3-L1 to get 208 3 phase out?
Thanks
jabuchol
(Jason)
10 February 2026 16:26
6
You run split phase from two legs of the 3 phase to double your voltage. It’s like 240 split phase.
chrigu
10 February 2026 17:09
7
208V threephase is three 120V sources in wye config. Same as the european 230V/400V, just with lower voltage
So to get that out of Victron units, you can follow the regular three phase stuff of the guide above
1 Like