Hello everyone! This is my first post and I signed up to clarify a doubt. I’m a newbie to this and I need to install a small solar system for a cabin that is on a family plot where I will spend 2 weeks a month for a period of several months intermittently. The system will be for a 45w fan, two 6w LED bulbs and a 55w mini freezer. The mini freezer is an inverter and is off most of the time. I have used it before. It is a 12v system and here are the components.
4 x 100w solar panels
BlueSolar MPPT 150/70
Phoenix 12/1200
200ah lifepo4 battery
Most likely I will connect two 200w series and then connect them in parallel so I would be getting 40v and 10a approximately. I would use a 16a breaker. I can also connect all 4 panels in series to get about 80v and 5a and would use a 10a breaker (these values are not real but it is an approximation of what I could generate with good sun)
I would use 10awg cable for a distance of 25 feet from the panels to the controller.
Now, here is where I have the serious problem. Due to the structure of the cabin the distance between the controller and the battery is approximately 18 feet. I read the manual and the controller should not be connected more than 5-6 feet away from the battery. I cannot raise the system to 24v because everything is already purchased and cannot be returned. And if I wanted to put the battery 5 feet away I have to break a wall in the room and the work and expense in construction materials would be very high.
I saw that through the Victron Connect App I can set the charging values that the manufacturer requires and I can also limit the amps that comes out of the controller. I was thinking of limiting the load to 35a. I bought the 70a controller because I really want to use half of its capacity the same way I bought a 1200 inverter to use less than half of its capacity. I don’t know what cable to use because I don’t understand the voltage drop very well. My biggest concern is not getting the terminals hot and avoiding a fire. What would you recommend? Can I use 8-6awg cable for 18 feet of distance limiting the amps to 35 or should I use 4awg cable? Any other information would be great. I’m still reading and educating myself but getting help would be great to get my project up and running as quickly as possible. Excuse the vocabulary but I hate gas emissions and I’m using a 1200w inverter generator and the smell of gasoline is already bothering me.
Thanks in advance.