I have a 3-phase ESS system and I’m experiencing
unwanted grid export despite having all zero-export
protections enabled. The grid meter (utility company
meter) registered a peak export of 72W.
System configuration:
3x MultiPlus-II 48/6500/100-50 (3-phase)
Cerbo GX MK2, Venus OS 3.73 (latest firmware)
JK BMS connected via CAN bus
VM-3P75CT energy meter (installed on grid input,
before MultiPlus AC-in)
SmartShunt 1000A
16S LiFePO4 battery, 16kWh / 330Ah
ESS Settings:
Mode: Optimized without BatteryLife
Grid metering: External meter
Multiphase regulation: Individual phase
Minimum SOC: 10%
Grid setpoint: 150W
Zero-export protections enabled:
AC-coupled PV feed-in: OFF
DC-coupled PV feed-in: OFF
Limit system feed-in: ON
Maximum feed-in: 0W
PreventFeedback = 1 (set via MQTT:
W/{VRM_ID}/settings/0/Settings/CGwacs/PreventFeedback)
MaxFeedInPower = 0 (set via MQTT:
W/{VRM_ID}/settings/0/Settings/CGwacs/MaxFeedInPower)
Both MQTT values confirmed via readback as correct.
What happened:
System was running normally with AC-in connected
Turned on a 3kW electric heater
System drew from battery (DCL limited to 30A)
and topped up from grid
Turned off the heater
VRM showed grid L1: -1044W (export!)
while L2: +112W and L3: +105W
Total grid showed -799W
This continued for approximately 30 seconds
I manually disconnected AC-in
Utility meter confirmed peak export of 72W
Note: No PV is installed in this system.
The export was from the battery, not PV.
Questions:
Why did PreventFeedback=1 not prevent
battery-to-grid export?
Does PreventFeedback only prevent PV feed-in
and NOT battery feed-in?
Is there a known issue with PreventFeedback
in Venus OS 3.73 on 3-phase systems?
What is the correct way to achieve absolute
zero export (including battery) in a 3-phase
ESS system?
Which grid code are you using? The standard power ramp in grid parallel is 400W/s, but the grid code could alter that, further reducing the ramp rate.
With your 3kW load switching i would expect the system to regulate to zero feed in/out in theoretically 7.5s, but realistically id go for 10s. In that time, import/export happens. Apart from physically disconnecting from the grid theres nothing you can do to avoid that.
Has nothing to do with this situation, but your battery is somewhat undersized for 18kW of inverter power. Id reconsider that.
AFAIK, EN50549-1:2019 does not define a ramp rate for regular use, only for special situation like reconnecting after grid failure, over/under voltage or over/under frequency events. For normal regulations it only defines that the ramp rate needs to be configurable by the DNO, but not an exact number.
If you look into the grid code settings, you can see the normal connect ramp rate, which is set at 100% in 0s, so in other words the 400W/s Victron standard rate applies. For your 18kW system, 45s for 100% would be the same as 400W/s. Further increasing the time only reduces the ramp rate.