I have a setup with a 90 kVA Victron Quattro, a Fronius 60 kWp Symo AC coupled, and a generator connected to Input 2. The Cerbo GX is configured to start the generator at 20% SOC. However, whenever the Cerbo GX starts the generator, the Quattro does not accept the generator at Input 2. Can you help solve this problem?
Have you ever looked here
Standard is input #1
Yes, after reading through this document, i disable LOM INPUT 2 then everything works perfect