Battery not charging; Status on Ekrano GX displays generator running on SOC
We just commissioned an AC Coupled system 90kVA comprising 6 unit of Quattro Inverter with Fronius PV Inverter.
We set Gen Aut-Start to trigger Generating set to start charging at 20% SOC, but unfortunately it doesn’t charge while the Gen set is running and the Elkano GX status already confirmed it’s running. Having checked, I confirm all parameters are on order.
Meanwhile, once the setup is manually bypassed it starts
charging.
Attached pictures.
Incoming frequency is 50.6Hz
Yes, it is programmed L1, L2 & L3 respectively
No, I didn’t try on charger only
Thank you Lado will check when I get to site this morning.
Meanwhile, will activating rare floating L1, L2 cause inverter from accepting charging?
Okay. Once I visit the site I will consider a reconfiguration and check the input cable sequence. Will revert on the outcome.
Thank you
Having visited the site, the only resolution is reducing the DC charging current and the entire setup resumes normal operation (Inverter accepts diesel generating set charging)
Meanwhile, I want to further ask out of curiosity what technical logic could warrant adjusting DC charging current on Victron Quattro Inverter before accepting power from diesel generating set to charge???
The instantaneous load on the genset can cause it’s power to go offspec, then the Quattro will reject it. Try ticking ‘Dynamic Current Limiter’ in the Quattro, which will wind up the Input Current to it’s set limit over a few seconds and give the genset a chance to adjust.
As an aside, the GX ‘Running’ indicator is only showing that it should be running. You can set it to alarm if it doesn’t actually start.
Thank you John
Noted.