Shore power at pedestal is 250/50 amp split phase. This runs to a Y cable splitting it into to 120/30 shore power supply’s. Those cable come into the boat and connect to 2 30amp elci breakers. 1 for each supply. I am attempting to recombine the neutrals after the breakers and connect the supply into a Multiplus II 2x120v. A soon as the multiplus runs through its start-up process it pops the breakers. Why does this setup not work?
Related topics
| Topic | Replies | Views | Activity | |
|---|---|---|---|---|
| Integrating MultiPlus-II 120/240 2 x 120 | 1 | 104 | 9 August 2025 | |
| Multiplus II 2x 120v rejecting shore power | 1 | 156 | 29 September 2024 | |
| Shore Power to Multiplus Positive In > Tripping House Breaker | 5 | 196 | 9 June 2025 | |
| Failure handling 50A 240v shore power AND single phase 120v Gen on a MultiPlus-II 2x 120V | 8 | 252 | 21 September 2024 | |
| How to wire AC input for 2 Multiplus II 12/3000/120 units configured in split phase | 0 | 12 | 25 February 2026 |