Ah, that makes better sense. He is correct you don’t need the smart meter.
Hi,
You akready setup the Fronius to use modbus on port 502 and enable Sunspec on id 126. There is nothing more to setup on the Fronius.
Make sure the Fronius and MP are both at the same phase, and it must be on L1. And that they are on the same LAN or Wifi.
Then at the console, go to Settings, PV Inverters, do a scan and see if the inverter can be found. Edit its settings and change the port to ACout. Then it will show up at the VRM dashboard.
thanks for the help!!
The Fronius is setup to use modbus on 502 and Sunspec on id 126. Both the MP and Fronius are on the same LAN.
I can’t change the phase settings and my system is single-phase. How can I remove the current PV inverter to then re-scan and add it?
In the same menu as where You did the scan, you can also delete the IP address that was previously assigned. Then rescan.
But do this when the inverter is only and is producing power. It will be asleep in the dark and will not respond to messages.