We have a Electrical connection (3F 400V +N) with an existing PV installation with SMA inverter 5kW single-phase connected to phase 1.
We want to buy a Victron Easysolar II GX 48/5000/70-50 MPPT 250/100 and connect it to phase 2 and connect 2 Batteries Victron 48V 100Ah 5kWh (total 10 kWh)
My question:
On the diagram I only see 1 current transformer to monitor the injection (because this is a mono-phase installation i think).
How can we measure the 3 phases (instead of only one) to control the Victron inverter and thus take into account the total injection or consumption?
Use a 3 phase grid meter
Recommended is VM-3P75CT, or EM540