I’m adding AC generator to my system, gonna use the victron VM-3P75CT to meter
where do I feed in the generator output? into the multiplus in or out, or skip the multiplus and direct to grid? I’m asking so the system counts the watts correctly…
I’m adding AC generator to my system, gonna use the victron VM-3P75CT to meter
where do I feed in the generator output? into the multiplus in or out, or skip the multiplus and direct to grid? I’m asking so the system counts the watts correctly…
What kind of system did you have ? ESS, island system, boat, RV?
ESS 3phase, wanting to add a small AC wind turbine to L1 for example
Ok, are your hole AC loads at AC out or AC in or mixed…
Do you have an overview plan about your ESS system?
yes entire ac loads on ac out
earlier I read the manual for the meter but there it didn’t say
so I have 3x multiplus, each one fed from 3f grid on L1, L2, L3
I can connect the 2kw ac generator to the ac input / L1 of multiplus #1? and put the meter clamp over that wire?
the turbine ac inverter synchronizes on its own with grid
Does the wind turbine inverter support frequency shifting / frequency watt meaning it reduces the power linear to increase grid frequency?
Ramp down shall starts at 50,2 Hz and reduce to 60% power at around 52Hz. Than it should shutdown.
If all is yes, you can put it to ACout like a grid compliant PV inverter.
Obey 1:1 rule. Tho it not further PV inverters on L1, depending on you MP2 size