Fideri K:
Use programmable relay assistant with a high power relay (I have some such relays lying around) with 2 conditions: 1. Switch on grid when SOC is below 20% 2. Switch on grid when loads exceed 9200W for 1 minute
There is a thread here.
gen for ac ignore.zip (911 Bytes)
@MotoringMariah that is quite the panel.
You will need to set your gen start stop on the gx to drive relay 1.
Program your parameters on the GX.
Import the above after unzipping. Adjust as the code by double clicking the node for the inverter as will be looking for my inverter still. There is a note there.
Summary
Deploy.
Test.
I had something else in mind but this seems simpler as you va basically ‘edit’ the code using the gx gui as you like. And have …
If you want zero grid charge maybe disable the internal charger on the inverter or use the one charge control assistant to be able to manipulate if you would like the option to do so at some point