DESS doesn't charge batteries full speed



It always plans to charge the batteries at full speed. But it seems to limit the maximum feed-in from the grid although it is not limited. This all happened since some other strange behaviour was shown as well. Which can been seen in other comments aswell. To sum it up: It charged the batteries throughout an entire night at 800W although DESS was enabled and it didn’t plan on doing so.

Today I tried disabling DESS and put grid feed in at 2kw, but it also didn’t do anything. I also restarted the vebus, but that also didn’t change anything.

Please help me, I’m lost.

When i change the minimum SOC of the battery at all times to above my current SOC it does charge at full speed.

If you are running Dess it is setting an amount of % for that hour to charge/discharge. If you have solar producion energy will not be taken from the grid (or less).
If you manually put the setpoint at 2000W it should charge. is your battery limited internally? is the BMS connected to the multi? how are you measuring SOT?

Heey Lars,

To sum it up:
I expect the Multiplus to charge my batteries at full speed. Our solar production peaks at 5kw and the multiplus 2 8kva needs about 6500W to charge at full speed. So I would expect the ac in to be 1500W + my consumption in our home. This is what is plans on doing and I have no clear explanation on why it doesnt.

This is today:

This is 2 days ago:

I expect my charge speed to lay much closer to 110A at all times.

For some reason when changing the minimum required SOC to higher than the current SOC the charging speed increases again.

My only guess as of right now that my 3d printer has something to do with this. It runs it’s own PID loop to keep the buildplate and nozzle hot, which might create a high frequency(1hz to 0.1hz) modulating power requirement that prevents the victron from drawing more power from the grid. To prevent overloading the charger. It’s the only thing that has been different from all other days.

Edit:
Forgot to answer some questions. Changing the grid feed in setpoint to 2kw, did not result in 2kw of grid feed in, At that time it was charging at 4kw. and only pulling about 500W from the grid. BMS is connected to the cerbo, but no limitations where given from the bms.

Hmm, strange. Especially that with the setpoint at -2Kw it is still not charging with this speed. A full reset? reload ess asistant, fetch latest firmware?

I have already updated the cerbo gx. Did not help. I have not reset or reloaded the ess assistant. Do you really think it would help?

I was using my 3d printer again today, I literally just turned it off but it still behaves the same:

It’s so strange, it’s the cheapest time of the day today yet it refuses to buy more electricity from the grid.

Hi Larsh,

Please check the datasheet.
The 8000 can charge with 110 Amps, wich is around 5200W. so this value is correct right?

Hi other Lars,


Yes as mentioned before, when the solaredge is not being throttled and this is the charging current I’m not to worried, it’s anywhere from 90 to 103A still not the advertised 110A, but close enough.

The problem however is when the Solaredge is on full power and being throttled:

Then my charging speeds are between 100A and 50A depending on my load, the Multiplus 2 simply refuses to take more AC electricity from the grid to charge the battery at full speed when for example the clothesdrier is on.

Hmm, that is strange tbh.. Dont know how that can happen actually

I have updated my Multiplus to v556 from v552 since I have read someone else had some problems with their generator aswell, In particular taking as much ac as it could, saying v555 solved his prolbems.

Redline is moment i updated it. Let’s hope it also solves my charging problem. In the graph you can see very well, how much my charging is throttled when my pv inverter is being throttled. You can also see that ac consumption doesn’t increase regardless of my selfconsumption.

Contacted my seller, They contacted Victron.

They didn’t give me a solution but it magically works again.
Yesterday before i reached out:(Grid feed in doesn’t follow consumption and doesn’t optimize charing)

Today after i reached out: (Grid feed in follows consumption perfectly and keeps charging at maximum)

A bit annoyed I still don’t know what happened, but glad it is solved.