Configuration of 5 panels to achieve the best performance (beginner question)
I am restructuring an old installation to set up a MPPT 100/30 and I have 5 Victron Energy 130 W panels:
  • Voc= 21.75V
  • Isc= 8.10A
  • Vpmax= 17.41V
  • Ipmax= 7.47A
If I connect all 5 panels in series, I get a high voltage and a low current. Would I fully take advantage of the MPPT performance, or would there be disadvantages?
If I connect 4 panels in a combination of series and parallel, I would have to leave 1 panel disconnected as a spare.
What would be the best configuration to achieve the highest performance?
Thank you for your help.
With 5x 21V panels in series you will destroy your MPPT.
Use MPPT Calculator - Victron Energy
You cannot do 5 panels in series with the 100/30, you would have to upgrade to a 150V MPPT.
The best you can do is 4 panels in series, which will give total Voc = 87.00 V, Vmpp = 69.64 V.
If you are in an extremely cold climate, you might be getting close to the 100V limit.
There is no reason to do series/parallel 2s2p.
Use the calculator linked above by BjoernK to be sure.