Hi All,
We replaced our 14 kWh Pylontech US3000C bank (failed in two and half years, what a horrible product and support) with a 16S EVE LF280K DIY pack + JK 150A active balancer BMS.
System:
- 3× MPPT 150/45
- 1× MPPT 100/20
- 1x SmartShunt 500A ( Connected to main battery negative)
- Cerbo-GX
- 2× Meanwell TS3000 inverters ( only for AC loads. not charging the batteries)
- ~7 kW solar, fully off-grid
- Also has DC system that directly powered from 48v bus
Settings:
- MPPT: Absorption 55.2 V, Float 54 V, Absorption 2h, Tail current off
- Shunt: 280 Ah, Charged 55.0 V, Floor 10%, Tail 2%, Eff. 99%
- CerboGX: DVCC on, SCS on, SVS on , others default, Battery Monitor: Smart Shunt
Now we don’t have BMS communication with Cerbo-GX anymore. (yet to purchase the kits for communication) and we have few problems with our system
- MPPTs often switch to float when SOC is only 70–85%. Is this due to low charge voltage
- One controller (always the same 150/45) shows a different charge stage than the others. e.g., in bulk while others are in absorption, or in absorption while others are in float.
- With long absorption on sunny days, it charge fast but BMS cuts charging (guess due to high voltage). On cloudy days, it only charge to 70-80%
- I thought DVCC will dynamically manage everything. but it seems MPPTs not really listening to DVCC
But other than these issues, New battery bank working fine.
What’s missing in my setup? I’d appreciate any help.