Samuel
Wiring in panel looks good except for lack of ferrules.
and it appears no ferrules on the NSI connectors in the junction box.
If you have a multi meter, set it to continuity (when you touch the two probes together you get a beep or indicator) and only proceed if you feel comfortable doing the steps below safely
wear safety glasses and have a buddy.
Turn off both inverters (using switch on front of each) and disconnect from shore power
Touch one probe to top left lug where white wires are and top right where green wires are in the panel, you should not have continuity, no beep.
This will test if there are any wiring issues inside the trailer, called a neutral isolation test.
if you get a beep / continuity, disconnect the two big green wires at the top right in panel and test again touching probe to ground bar where the wires were in the panel and the white wires on the left.
if you still get a beep you have a wiring issue in the trailer, if you don’t you have an issue with the inverter ground relay.
If no beeps above then connect your 120v shore power cord to a GFCI outlet and it should not trip.
then turn on to charge only the inverter with AC2 connected only and see what happens.
You should have a GFCI on the load side of the inverters, either GFCI outlets, but that won’t work for your 30amp and 240v circuits, so a GFCI between the inverters and the panel would be easiest for your setup
https://www.homedepot.com/p/Square-D-QO-60-Amp-2-Space-4-Circuit-Spa-Panel-Main-Lug-Load-Center-QOE260GFINM-QOE260GFINM/312035158
or equal GFCI breaker wired between your inverter and panel
(you cannot replace the existing 50amp main breaker in your panel with a GFCI breaker, because you cannot back feed it, it will need to go in another enclosure like the attached link)
or switch the breakers in your panel to GFCI breaker you have room but some will need to move to the other side as GE does not have a slim line GFCI breaker, also GE is now ABB in case you have trouble finding breakers
https://www.homedepot.com/p/GE-20-Amp-1-Pole-Ground-Fault-Breaker-with-Self-Test-THQL1120GFTP/206602317
https://www.homedepot.com/p/GE-30-Amp-Double-Pole-Ground-Fault-Breaker-with-Self-Test-THQL2130GFTP/206602329
could add GFCI outlet to the 20amp 120v circuits and breakers to the 30 and 240v circuits, to save cost.
An electrical contractor in your area could help you with this if beyond your comfort level.
Ian and Ed
5ma is for life safety , because 10ma is the let go threshold, meaning at 10ma of current you can no longer let go, at 30ma you have respiratory paralysis and can no longer breath. Above that you get ventricular fibrillation, so defeating or “designing around” this “nuisance” is not a good idea.
In re to EU being safer, they still have shelter in place as the standard in some areas during a building fire. The issue is two different electrical system and codes. RCDs are considered supplementary circuit protection and in most cases protect all of the circuits in a panel not just a single outlet so 30ma is a compromise to avoid nuisance trips at the cost of life safety. There are also varying earthing requirements across Europe, some areas have floating neutrals being the building earth is not bonded to the utility neutral so an RCD is critical to detecting and protecting from a line to earth short but they are set to 100ma, RCD are primarily for supplementary protection with a bonus of some life safety.
But I’m getting ready to celebrate treason day and my independence from the above electrical system so my thoughts maybe biased.
Also AC gives you a chance 50 to 60 times a second to let go, DC does not, DC voltages above 50volts can kill well before the 100s of amps fuse trips just FYI.