Dear Victron R&D Team, as already discussed with the community I found a condition which causes false disabling of AC coupled inverters (Fronius Symo in my case). If the grid fails asymmetrically and the phase of the master Multi is still present, the system increases the MG frequency periodically to 53Hz. I suppose the system prepares itself for grid synchronizing and reconnect (cannot provide FSPC any more and therefore disables inverters) without checking of other 2 phases. In case of such grid failure the AC coupled inverters are not available and the system doesn’t fulfill its function properly. Could you fix it and provide a firmware update? Thanks.
Related topics
| Topic | Replies | Views | Activity | |
|---|---|---|---|---|
| Trying to understand MultiPlus II phase shift behaviour | 2 | 158 | 31 December 2025 | |
| Multiplus II ESS with Fronius Gen 24 on AC out | 2 | 230 | 31 July 2025 | |
| Microgrid periodically rises frequency to 53Hz | 7 | 115 | 23 November 2025 | |
| Ac coupled PV inverters stop working when ESS loses grid connection | 6 | 265 | 20 December 2025 | |
| Multis erhöhen periodisch MG Frequenz auf 53Hz und deaktivieren Fronius | 13 | 179 | 24 November 2025 |