BMV + three phase quattro parallel system

Greetings Victron community.

I have a three-phase parallel quattro 8kW inverter system and a battery bank not compatible

to the victron system.

I would like to install a smart BMV but I cannot find any three-parallel victron diagram with a BMV incorporated.

Can someone assist.

Regards.

Differences on the AC side of the system are largely irrelevant for the battery monitor. One side of the shunt connects to your primary battery bank negative and the other side connects to ALL DC loads and sources. If you only have Quattros and MPPTs in your system you could also just use the battery monitor built in to the Quattros.