Hi All,
I am experiencing severe system instability with the 3-phase ESS setup.
Setup:
- 3x MultiPlus-II 48/5000/70-50
- Cerbo GX
- Pylontech US5000
- Victron VM-3P75CT (Grid meter)
- 2x 1-phase 5 kW PV inverters + 3-phase PV meter
Ever since a recent grid outage and utility intervention by Fluvius, the system goes wild whenever the MultiPlus units are active with ESS enabled:
-Wild power swings: The system enters a heavy feedback loop. MultiPlus units rapidly swing between max charge (+130 A) and max discharge (-130 A) every few seconds.
-Incorrect meter readings: Grid readings bounce wildly between +10 kW and -10 kW. In Venus OS, AC Loads drops to 0 W because it detects a massive fake grid export (-9.7 kW) while the house is actually drawing power.
So far, the main grid meter was replaced with a new Victron VM-3P75CT. With the MultiPlus units off, all three phases read correctly with correct signs. When the MultiPlus units are turned OFF, all grid, PV, and house consumption readings immediately stabilize and show 100% accurate, real-time values.
Since the PV setup consists of two single-phase units on a 3-phase meter (producing energy only on L2 and L3), I suspect a phase mapping / rotation mismatch between the grid meter, PV meter, and MultiPlus AC-In terminals.
Questions:
- Could a phase mapping mismatch on an external PV meter cause the ESS algorithm to trigger feedback loops of this scale (±10 kW)?
- What specific parameters or diagnostics in Cerbo GX or VEConfigure should be inspected to locate the exact cause of this control loop oscillation?
- Could an internal phase-angle or voltage sampling calibration on AC-In have been corrupted by the grid surge?
Thanks for any help or advice!