Apologies for the length, but I wanted to ensure I provide adequate context. I am working on a food truck that will operate all its equipment from a battery-based system. Below, I have outlined the system specifications, the proposed setup, and a few technical questions
System Overview:
We are aiming to run the entire food truck operation electrically, with a 48V / 80kWh battery system, which must be fully charged daily. A 3kW solar array is available, but it alone cannot meet the daily charging requirements, hence the need to integrate a Level 2 EV charger for supplemental charging.
System Components and Configuration:
- Battery Configuration:
- Five (5) 48V x 16kWh batteries
- Each battery lands on a Victron Lynx Distributor, aggregating to power a 15kVA Victron Quattro inverter/charger
- The Quattro’s maximum DC input current is 350A @ 48VDC
- Charging Source:
- A ChargePoint Level 2 EV charger providing 50A @ 220V
- Capable of charging the battery system from 10% to 90% in approximately 7 hours
- Grounding:
- The neutral-to-ground bond will be disabled on the Quattro to allow for external bonding control
- Load Requirements:
- Max 160A @ 240V
- Max 50A @ 120V
Proposed Setup:
Input Side:
- The Level 2 charger will supply 50A @ 220V via two hot wires and one ground wire to a J1772 Type 1 Socket Inlet (preferred).
- An optional secondary shore power inlet (also 50A @ 220V) may be installed.
- Both inlets will exclude a neutral conductor for safety considerations.
- An Automatic Transfer Switch (ATS) will manage the switch between shore power and EV charger input.
Output Side:
- Each of the Quattro’s AC outputs will connect to a 100A Victron Autotransformer.
- Configuration: 2 x 100A @ 220V and 2 x 32A @ 120V
- both autotransformers outputs will feed into the main AC breaker panel.
Technical Questions:
- Input Side Safety:
- Is this input configuration (two hot wires and ground only, without neutral) safe and compliant, particularly with the use of a J1772 inlet and ATS?
- Equipment Grounding:
- Given the high voltage and current in the system, is it safe and advisable to bond equipment enclosures (such as inverter housings, breaker panels, transformer casings) to the vehicle chassis?
- Neutral Bonding Strategy:
- Since the grid input does not supply a neutral, and the only neutral exists on the output side of the autotransformers, do I still need to establish a neutral-to-ground bond in the AC breaker panel?
- If so, what are the implications of bonding in the panel while the system is charging or in passthrough mode? Is there a risk of back-feeding or ground loop issues?
- Autotransformer Isolation:
- What is the recommended method to **wire the two autotransformers outputs ** to the AC breaker panel in such a way that, if one transformer shuts down or fails, power from the other transformer does not back-feed into the inactive unit?
Thank you very much for your time and assistance.