OK So I have my system set up in my motorhome. I have a 48v 15kva Quattro 230v (configured for 240v, 60hz) outputting to a 100A auto-transformer to take the 240v single phase off AC Out1 and convert it into 120/240v to my 50A panel. I also have an onan 8Kw QD 120v (2 legs, 120v in phase 30A ea and I have the bonded together at a bus bar) going to a second 100A autotransformer to step the 120v 60hz single phase to 240v 60hz single phase. This goes into AC-1 IN configured as a generator, then outputs to AC Out - 1 which goes to the AT being used to create split phase.
When in inverter mode running off the solar and batteries, the quattro and autotransformer kick the ground relay on the AT on, and provide power, no issues everything works, no ghost loads.
When I turn on the generator, the AT1 energizes, the ground relays kick off, but only half the load goes to charging the batteries, the other just dumps into AC out1 when there is no load there. Example. When the inverter is running, then I have 588watts going to AC out. Once the generator comes on, and say I’m generating 4kw on it, 1800watts will start loading up on AC1 out, though nothing changed on the load side, and the rest will go to the batteries.
I have removed the neutral ground bond at the genset, and I have checked continuity. no tone, and reads zero. Voltage going into the first AT is 120v, coming out is 240v and it reads 240v going into the quattro from VRM. If I reduce the amp limit, and I’m producing 2kw on the generator, then the load going to AC-1 will scale down accordingly, to about 1kw. Can someone please help me figure out what is going on? If i put it into charger only mode, and shut off AT 2, then all load goes to charging the batteries.
Long term, I’m going to try to sell the generator, and pick up a 12.5kw onan that is 120/240 and then I can just connect the two hots directly to the quattro and bypass the AT. But in the interim, I would really like to figure this out and have it work.