Yacht setup with Older Multiplus, Mase Genset Auto Start/Stop?, SoC accuracy and AC Input 1 ignored

Thank you for that link and for taking the time to answer, it is much appreciated.:

Based on what you wrote I have checked and here is how the settings were configured:

  1. Set to 600Ah, so correct
  2. Was set for 27.4V so low, have reset to 28.0V
  3. Correctly set at 4% (equates to 24A)
  4. Charged detection time was 5 mins, have now set to 6…
  5. This has changed in the app, options are now “Keep SoC” “Clear” and “Set to 100%”, was on “Set to 100%” now on “Keep SOC”
  6. In the 2 solar controllers expert mode is not enabled, so I would need to enable it to alter the Tail Current option. 4% of 600Ah is 24A so my assumption is that I could set the Tail current to say 20A in each solar controller and that would meet the criteria, or do I need to set each one to 10A to give a combined 20A?
    I have attached (hopefully) a screenshot of what it looks like before I make any adjustments.

Again, many thanks, I will see how it does tomorrow