Hi Everyone! This is my first post.
I am spending some time volunteering at a hospital in rural Malawi. In 2022, in a project funded by donations, a grid-tied ESS with a sizeable solar array and battery bank was added, stabilizing the power supply for the hospital and providing backup power during all-too-frequent utility outages. The battery bank was added onto in 2024, increasing the storage capacity. I am coming in as a residential electrician from the US, doing my best to learn about the system from Victronâs website, and Iâve finally hit the point where I have some installation-specific questions I canât figure out on my own.
The system described briefly:
-
3-Phase 230V 50Hz Grid
-
6x Victron Quattro 48/15,000/200 - configured to 3-phase
-
7x Fronius Symo 15.0-3-M - one on AC Input, six on AC Output
-
45x Leoch 48V 100Ah LiFePO4 batteries, arranged in banks of 5, with a Victron BMV-700 monitoring each bank of 5
-
Victron Cerbo GX Controller
Lately, Iâve been looking into battery health and State of Charge readings, to make sure we are doing all we can do to take care of the investment and get the most out of the system. To do this, I have been using the built-in display on each individual battery to get capacity and SOC readings and then comparing that to the BMV readings. Below is a data set from this morning.
| Bank | Battery | Model | SOC (%) | FCC (Ah) | Rm (Ah) | Cycles |
|---|---|---|---|---|---|---|
| 1A | BMV-700 | 53.3 | ||||
| 1 | Averge LFELI-48100TB | 47.46 | 93.1 | 44.2 | 703 | |
| 2 | Averge LFELI-48100TB | 51.38 | 100.0 | 51.3 | 696 | |
| 3 | LEOCH LFeLi-48100CB | 55.9 | 90.8 | 50.8 | 1057 | |
| 4 | LEOCH LFeLi-48100CB | 51.11 | 101.4 | 51.8 | 1070 | |
| 5 | LEOCH LFeLi-48100CB | 47.77 | 87.3 | 41.7 | 1029 | |
| 2A | BMV-700 | 53.3 | ||||
| 1 | LEOCH LFeLi-48100CB | 52.81 | 99.5 | 52.5 | 997 | |
| 2 | LEOCH LFeLi-48100CB | 44.69 | 83.3 | 37.2 | 1072 | |
| 3 | LEOCH LFeLi-48100CB | 56.82 | 108.7 | 61.7 | 917 | |
| 4 | LEOCH LFeLi-48100CB | 55.74 | 98.8 | 55.1 | 943 | |
| 5 | LEOCH LFeLi-48100CB | 56.07 | 100.9 | 56.6 | 1109 | |
| 3A | BMV-700 | 58.7 | ||||
| 1 | LEOCH LFeLi-48100CB | 50.28 | 90.9 | 45.7 | 936 | |
| 2 | LEOCH LFeLi-48100CB | 52.06 | 64.6 | 33.6 | 1121 | |
| 3 | LEOCH LFeLi-48100CB | 52.96 | 74.8 | 39.6 | 1141 | |
| 4 | LEOCH LFeLi-48100CB | 40.73 | 80.1 | 32.6 | 975 | |
| 5 | LEOCH LFeLi-48100CB | 54.76 | 102.0 | 55.8 | 959 | |
| 1B | BMV-700 | 53.5 | ||||
| 1 | LEOCH LFeLi-48100CB | 49.7 | 100.0 | 49.7 | 936 | |
| 2 | LEOCH LFeLi-48100CB | 51.39 | 101.3 | 52.1 | 986 | |
| 3 | LEOCH LFeLi-48100CB | 52.49 | 69.0 | 36.2 | 1032 | |
| 4 | LEOCH LFeLi-48100CB | 54.51 | 97.3 | 53.0 | 764 | |
| 5 | LEOCH LFeLi-48100CB | 54.1 | 102.5 | 55.4 | 821 | |
| 2B | BMV-700 | 54.1 | ||||
| 1 | LEOCH LFeLi-48100CB | 56.05 | 92.0 | 51.6 | 1040 | |
| 2 | LEOCH LFeLi-48100CB | 48.44 | 88.1 | 42.6 | 1054 | |
| 3 | LEOCH LFeLi-48100CB | 48.3 | 94.5 | 45.6 | 1102 | |
| 4 | LEOCH LFeLi-48100CB | 50.87 | 101.3 | 51.5 | 1123 | |
| 5 | LEOCH LFeLi-48100CB | 50 | 94.9 | 47.4 | 1077 | |
| 3B | BMV-700 | 51.6 | ||||
| 1 | LEOCH LFeLi-48100CB | 43.64 | 83.2 | 36.3 | 1082 | |
| 2 | LEOCH LFeLi-48100CB | 49.79 | 100.0 | 49.7 | 1161 | |
| 3 | LEOCH LFeLi-48100CB | 52.13 | 101.5 | 52.9 | 1107 | |
| 4 | LEOCH LFeLi-48100CB | 54 | 102.6 | 55.4 | 1060 | |
| 5 | LEOCH LFeLi-48100CB | 55.05 | 102.9 | 56.6 | 1026 | |
| 1C | BMV-700 | 51.4 | ||||
| 1 | Averge LFELI-48100TB | 50.68 | 100.0 | 50.6 | 654 | |
| 2 | Averge LFELI-48100TB | 50.36 | 100.0 | 50.3 | 645 | |
| 3 | Averge LFELI-48100TB | 42.76 | 87.6 | 37.4 | 650 | |
| 4 | Averge LFELI-48100TB | 49.23 | 100.0 | 49.2 | 663 | |
| 5 | Averge LFELI-48100TB | 50.5 | 100.0 | 50.0 | 639 | |
| 2C | BMV-700 | 53.3 | ||||
| 1 | Averge LFELI-48100TB | 51.69 | 100.0 | 51.6 | 686 | |
| 2 | Averge LFELI-48100TB | 43.43 | 87.4 | 37.9 | 723 | |
| 3 | Averge LFELI-48100TB | 50.41 | 100.0 | 50.4 | 647 | |
| 4 | Averge LFELI-48100TB | 51.35 | 100.0 | 51.3 | 656 | |
| 5 | Averge LFELI-48100TB | 50.68 | 100.0 | 50.6 | 662 | |
| 3C | BMV-700 | 55.2 | ||||
| 1 | Averge LFELI-48100TB | 46.46 | 90.2 | 41.9 | 673 | |
| 2 | Averge LFELI-48100TB | 50.97 | 100.0 | 50.9 | 663 | |
| 3 | Averge LFELI-48100TB | 51.54 | 100.0 | 51.5 | 668 | |
| 4 | Averge LFELI-48100TB | 51.86 | 100.0 | 51.8 | 653 | |
| 5 | Averge LFELI-48100TB | 48.95 | 96.0 | 47.0 | 664 |
Two things stand out to me:
The first thing that stands out is that the SOC values registered by the Victron BMVs donât seem to correlate to any values given by the individual batteries. Taking bank 3C, for instance, if I sum the remaining charge and divide by the sum FCCs, I get an overall SOC of 50.0% for the bank. Or, if I divide the amount of Ah depleted by the 500Ah bank capacity as configured in the BMV, I get a calculated 51.38% SOC. However, the BMV itself reads 55.2%. Can anyone help me account for this difference? Or help me understand which value is most accurate? If there are settings that need to be tweaked (such as updating battery capacity in Victron Connect), what are they?
The second thing that stands out is that the full-charge capacities of the individual batteries have some serious outliers! Many batteries, both new and old, still register very close to their initial 100Ah capacity. However, one older battery is now as low as 64.6Ah, and even two newer ones read 87Ah! What is to be made of these differences? Is it normal for batteries to differ so much individually, and is this expected performance for 2 and 4-year old batteries? If not, what are some things we could try to improve the lifespan?
For context, all batteries are connected in parallel using a Victron Lynx Distributor busbar system. They are in an air-conditioned room with air-conditioners running constantly. Since I have been at the hospital (2 months now) the batteries are scheduled to charge to 100% once per week, but they often reach 100% anyway on sunny afternoons. They are set to self-consume down to 45% each night, but we consume down to 20% during nighttime outages before using the generator.
As I said initially, I am new to Victron products and to this forum, so in addition to help with the above questions I would also love to be connected to any resources in general that would help me learn more about the hospitalâs system. Thank you in advance for your help!
Matthew
(Photos of the system below)