I am using a MultiPlus-II 48/5000/70-50 in ESS mode.
Attached are
via DC: 2 x SmartSolar Charger MPPT
via AC-OUT: AC PV Inverter
two 48V batteries
A raspberry Pi running VenusOS large
Is there any way to charge the battery using DC only?
I have tried the following using Node-Red:
-1- Set “ESS max charge power (W)” to zero. Setting this disables charging not only via AC but also prevents charging via DC.
-2- Set mode to MP2 mode “1: Inverter only”. Unfortunately this disconnects AC-IN. Thus the AC PV Inverter can not be used any more except on AC-OUT.
Is there any way to disable the charger via AC on the multiplus without disconnecting AC-IN?
-1- In node-red, there is is the possibility to “disable charger” (ESS-control, Multiplus II, “disable charger”).
-2- In VE.BUS System/Multiplus there is a “disable charge flag”…
Both disables the charger. But unfortunately this also disables charging via Victron MPPT (DC).
I will try what happens if I disable the charger in VE-Config.
Any way to disable the internal MP2 charger so that I only charge vie MPPT (DC) and not using AC?
And yes, I am using the actual firmware of the MP2: v552
Are you on-grid or off-grid?
Is the PV Inverter support enabled in the ESS Assistant or the is the PV-Inverter assistant installed?
(Is the feed-in of AC PV enabled in the GX ESS settings?)
On-grid it shouldn’t use AC PV to charge the battery.
Off-grid the AC PV energy has to go some where.
With the PV-inverter support enabled it would increase the frequency to throttle down the PV inverter.
Not sure how it will react without the PV-inverter support, I guess it will not increase the frequency and uses AC PV for charging but it will shut down at some point to protect the battery from overcharging.
This didn’t work for me. An external inverter connected to AC-IN charges the battery via AC even when the internal charger is not enabled, I wanted to stop this.
Maybe you connected your inverter to AC-OUT? In this case, the internal charger is not used on ESS.
If you connect it this way (which is needed in my configuration) disabling the internal charger on VEConfigure does not have any effect. Only setting “Charge Current” to 0 does the trick.
Whatever it is. The solution by setting “Charge Current” to 0 works.
I played with the settings. And can replicate the over ride.
If you set ESS to keep batteries charged it will use the internal charger even when it is disabled in settings. (Not set to zero amps)
But using optimised with battery life even set at 100% it does not charge the battery.
Then looking at all the systems I had previously just disabled the internal charger on and realised none of them use keep batteries charged, which is why it was never noticed before.
So thank you @herzigwi. Appreciate the contribution. I have learned something new.
Thanks. I think I tested this before, but of course I will test it tomorrow again. As far as I remember this will also disable MPPT charging via DC. I only want to disable AC charging. Means I only want to disable the internal multiplus charger.
I would use node red- switch it to keep batteries charged using soc switching and back to optimised when the desired soc is reached off grid charging.
Leave it disabled in the ve config.