VICTRON ISOLATION TRANSFORMER 7000 W ~230 V INSTALLED IN THE US
(I will refer to this device as “The TRF”)
1…
In this case a US Marina transformer, single phase with a middle point on the output windings. It is customary to bond ( To ground) Neutral with PE Earth:
L1~L2 = 240 V
L1~N = 120 V
L2~N = 120 V
L1~PE = 120 V
L2~PE = 120 V
PE~N= 0 V
2…
What could happen if the dock PE wire is connected to the PE Input terminal of the TRF ?.. presenting:
L~N = 240 V
L~PE = 120 V
N~PE = 120 V
Are installers, leaving the PE Wire disconnected between the boat shore inlet’s receptacle and the TRF Input, using a Residual Current circuit breaker 2-pole.?
If in an input failure the TRF enclosure becomes energized, the enclosure will discharge through its M4 welded stud at the bottom of the TRF enclosure towards the dock through the boat handrails or submerged metal parts and trip.
The residual current circuit breaker may fail, and not trip killing a person?
What about active galvanic current under 20 ma continuously entering from the Dock Line to the boat bonding system?
3…
Does the transformer contains any internal device causing similar results to the Victron Multiplus ground relay?
What is connected internally after the Input PE Terminal? The soft start internal circuit? The cooling fan? or any electronic component that could fail in a closed position creating a path to the enclosure?
ANY HOW
4…
Measured continuity (In a disconnected, uninstalled TRF on its box) with an ohmmeter, between the Input PE terminal to all other terminals and enclosure, and there is no continuity towards anywhere, concluding that “it is an isolated point”.
Probably Victron Answer is:
“The Input PE Terminal is ONLY used to install the jumper towards PE Output when the boat is hauled out of the water”.
But I am not sure that is all, or if there is more than that?
5…
EVEN WHEN THE DOCK PE WIRE IS CONNECTED TO THE TRF INPUT PE TERMINAL:
When a failure in the TRF’s input side energizes the TRF enclosure, the TRF Input PE terminal DOES NOT COME CONNECTED TO ITS ENCLOSURE FROM MANUFACTURING, so there is no a cable path for failure current to flow to the doc.
Meaning Same thing, WITH OR WITHOUT, connecting the dock PE Wire to the TRF PE Input Terminal… the discharged failure current will have to exit the M4 Stud Welded on the Bottom of the TRF.
Failure on the bonding system will endanger life
Correct?