Hello! I want to see full info about Victron fuse 200A MEGA - 80v. I need to know fuse tripping time and others important data. Where I can find it?
Product pages at the bottom, there are datasheets.
Ok, but there are no info about AIC or “let-through energy” and I really can`t understand this fuse would be fast enough for inverter and battery protection or not…
The mega fuse when properly installed will manage a 200A load continuously.
What are you trying to fuse?
A fuse is an overload/short circuit protection for the wire, not for the connected device.
I think the real question is how much the breaking capacity of the fuse is (in kA).
Edit: 2kA (2000A)
So the application now is important to know.
Lithium battery bank or a device?
There is no arc quenching like with the NH and T series so if that is important then do not use mega fuse.
That’s why I always use large DC breakers between batteries and the rest of the system, followed by fuses.
Many thanks! Now I know that this fuse is not enough for my system.