I was running a SmartSolar MPPT 150/70-Tr VE.Can with 1,86kWp (south oriented) since 2018.
In June I got 12 Solarpanles Longhi 455Wp.
Last month I installed the two new SmartSolar MPPT 250/100-Tr VE.Can where I use Strings of 4 in series where the first one has 3640Wp and the second 1820Wp (I will get 4 more modules) and all are installed side by side west oriented to get in the Winter more sun.
However, my Energy readings are strange, because the second one produce lesser then 33% of the first one, while it should produce 50%.
Cabling as ABSOLUT identical (25mm2, same lenght of cables, all three VE.Can are shown in ColorControl GX).
Yes that would be the easiest to start getting an idea.
If then the other mppt shows this effect, it could either be due to efficency-reasons, OR one of the panels in the only-4-panel-string could have a ditch as well.
To figure that out, you then could disconnect 4 of the 2x4-String and compare both mppts by running a 1x4 each. (Considering all the 8 panels in the 2x4 as “healthy base” to compare with)
It seems, the reason is NOT the overpowering of Solar_2 (3640Wp) vers Solar_3 (1820Wp) but that the SmartSolar is working better under full load.
I have tested all three MPPTs with only 4 modules (the 150/70 wad running with 2x2 while the 250/100 had 1x4) and the 150/70 outperformanted the 250/100
Makes sense, the 150 has less bucking to do to get down to 48V nominal, versus the 250s and 450s.
When I compared my 150/35, 250/100 and 450/100 (different panels but same point in time), results seemed to match Victrons stated efficiency specs (150>250>450). Losses on the 450 were about double the 250.
I have the impression, that the promised efficiency is only under full load, hence you NEED to overpower the MPPT by at least 10%
1860Wp on a 150/70 is sub optimal, but smaller CAN versions do not exist. Unfortunately I bought it around 3 month before the 250/70 came out. However, I think on change the 150 to a 250, since 6 modules have only 228Voc and the 250V just fit.