I am getting spurious battery high voltage alarms. The max battery charging voltage is set to 57.6 V but I get alarms/notifications at less than 57 V. I cannot find any way to turn off these spurious alarms/notifications. Any ideas?
Similar issue. Can’t seem to find a way to turn them off completely or at least temporarily.
You can now switch off specific alarms in guiv2 on OS v3.55
Device list - inverter - alarm set up
I will be surprised if that works. The high voltage alarms are coming from the battery, not the inverter. I may try disabling the inverter “High DC voltage” alarm. But not within the next several days because it will be cloudy and the battery will not reach full charge.
FYI the option is also available in GUI V1. I am not a fan of GUI V2 but that’s not something to talk about more in this thread.
Good to know. To be honest i didn’t look.
I misunderstood this.
Are there cells high at the time of the warnings?
Actually looking at the list of past notifications they all say:
Pylontech battery
Warning
High cell voltage
So the alarm is due to high cell voltage according to the battery itself. I have DVCC enabled and a CAN bus connection between Venus OS and the battery.
(Strangely all the recent notifications do not include the battery voltage. I did recently upgrade Venus OS so something may have changed regarding how it interprets messages from the BMS.)
The battery (actually two 5 kWh server rack batteries in parallel) is actually from SOK Battery. Apparently they speak the Pylontech protocol so Venus OS detects them as Pylontech batteries.
But all this is really irrelevant. Since I have enabled DVCC the battery should be controlling charging. The cell high voltage warnings are of no value since the BMS is controlling charging and there is nothing I can do to change BMS charging parameters. (I have tried changing the maximum charge current and voltage in the DVCC settings but they seem to be ignored by the BMS.)
So back to my original question at the start of this thread. Is there any way to turn off notifications in Venus OS? (I don’t think so.) The management of notifications should work something like it does on my phone IMHO. (I have managed to turn off the extremely annoying notifications from VRM.)
Not entirely true. It is useful for early diagnosis of issues in banks. Particularly if they are repeat cells.
From the GX side there isn’t an easy way to stop these.
At 57.6 that is 3.6v per cell pretty high i am not surprised you are getting high voltage issues. As that is at the end of the cell voltage range already.
Couple that with slower balancing and you will have issues.
Does the bms vary the ccl and the voltage limit natively. Or does the voltage stay up at one value?
The voltage cap in dvcc works for all batteries.
SOK Battery recommend 57.6 V (3.6 V per cell) for absorption voltage in open loop configuration. Maximum 58.4 V (3.65 V per cell). My understanding of LiFePO4 is that these are widely accepted values.
I have set the charge current limit (CCL) to 60 A. I have seen the CCL change to 47.5 A in the battery parameters. Usually it is 190 A which is twice the 95 A per battery limit specified by SOK Battery.
I have set the charge voltage limit (CVL) to 56.5 V. I have never seen the CVL change. It is always 57.6 V. So the battery sends high cell voltage warnings but doesn’t back off the CVL. Weird.
Yeah. Pylon remains at 53.2v. 3.54v per cell. Some cells may overshoot this voltage which is when the high voltage warning/alarm appears. I have found on older banks they dtart way sooner than that as well. (So get more annoying)
Most battery manufacturers actually vary both the CVL and CCL pylon don’t seem to.
A concern with them allowing it to run that high is then the cells may overshoot the 3.6v which is already the outer range of the cell nominal use limits.
How have you set the ve bus and mppts absorption and float? Have you kept in with the trend of setting them lower as would normally be done for pylontec?
I guess altered for 16s it would mean about 55.5v absorption and 54.4v for float.
Are you feeding back to grid or setting your system to keep batteries charged?
I’m not sure I should follow any recommendations for Pylontech batteries. As I said previously the batteries are actually from SOK Battery. Maybe SOK Battery use the exact same BMS as Pylontech but I don’t know that for sure.
I have set the MPPT solar chargers to the values recommended by SOK Battery. But both solar chargers show their state as " Ext. control" which shows that DVCC is overriding any charge settings I have put into them.
I don’t have any grid or generator connection so inverter charger settings are not relevant.
As per my previous post I don’t have any grid or generator connection.
Just needed some clarification there. You have no previous posts showing in your history.
Ok. When do the alarms start or are at their worst?
I have seen other forums with users setting their voltages lower with some success.
Maybe try a shorter absorption. Or editing the SOK parameters. There are other forums where users have done this and had success in taming the HV alarms.
They are generated by the BMS and sent to the system.
I think we have a terminology confusion. By “previous post” I meant something I had posted previously in this thread.
When the battery is at or above 99% SOC and voltage is also at around 57.6 V.
There is no DVCC absorption time setting. This makes sense because charging parameters are (mostly) controlled by the BMS when DVCC is enabled.
I have not found any way to edit SOK Battery BMS parameters. Do you have a link to a site which describes how to do this?
Yes. This I know and that’s why I want a way to manage notifications.
Well it seems I have misunderstood how DVCC works. Today I have enough PV power to get to full charge and I noticed that the battery voltage was below the limit I had set in DVCC settings. So I increased the DVCC “Maximum charge voltage” a couple of times and each time the battery voltage increased to around 0.1 V below the limit. Currently set to 57.4 V with no high cell voltage warnings.
My mistake was thinking the battery CVL should change. It doesn’t but the DVCC voltage limit overrides it. So my battery is still asking for 57.6 V but DVCC is only allowing 57.4 V.
So for anyone reading this thread in future please disregard anything I have said about DVCC not working.
I spoke too soon about the 57.4 V charge voltage limit. Still too high so it is now 57 V. Remains to be seen if this is low enough to avoid high cell voltage warnings.
They consider their batteries charged at 55.2v (from their smart shunt set up guide)
Clamp it down around 55.5v in DVCC. And then raise it to 56.5v. Thier own manual recommended method for taming the warnings.is using dvcc.
Set a very short absorbtion time in settings (15mins) if you want to keep the outer end charged voltage programmed.
I definitely don’t like their cell voltage range use. It colours outside the lines a bit from conventional norms. And I do not think their balancing methods are aggressive enough for their use choice. Which is probably why it is overshooting in total pack voltage and cell voltage.
Maybe so. But that is not what the battery manual says. 55.2 V is the float voltage. The absorption voltage is 57.6 V. I guess you could interpret 55.2 V as the voltage after a battery is fully charged but that doesn’t happen until after the absorption phase.
I don’t think you can set absorption time in DVCC.
One thing I have seen when I was not using DVCC was that cell imbalances did not show up until about 3.6 V per cell. So not allowing the charge voltage to get somewhere near this would mean balancing would never start.
No, that is done in base settings on the inverter and mppt.
There is not much capacity gain after 3.5v so cell voltage rises fast (and falls fast) after that.
The cells should be balancing long before that. If they aren’tthen that is a poor bms cell management situation.
I read through the discussion, and my view is that the software from your battery is not good enough to avoid one cell going to high and you get an alarm.
Your battery should react actively and faster that one cell is climbing to the higher voltage, AND should regulated the CCL and/or CVL quicker to a lower level.
Best to ask your battery supplier for a new firmware version to solve the issue.
Setting a lower voltage will avoid alarm, but maybe the batteries don’t balance so good as should be.