Hi, I have the 2 phase system with following setup: 2 x MultiPlus 48/3000/35-50
1 x Venus GX
1 x MPPT 150/70-Tr
1 x Lifepo4 Battery box 48V system 16x314Ah with JK BMS.
I must admit I’m not a great technician, trying to learn the things. I bought this DIY battery box, successfully assembled. On Sunday I managed to connect the battery box to the inverter and establish a communication between Venus and JK BMS. Happy life!
Of course the battery was never charged to 100%, the JK BMS was not calibrated and showed around 60%.
On Monday everything was running OK. But today morning (Tuesday) I woke up and saw the system shoot down (error #38) I assume due to low battery voltage (I received a bunch of alerts).
I managed to revive the system. But since then the Multiplus shows SOC 100% and won’t charge the battery and still getting low battery alert.
I tried to change the battery monitoring from automatic to JK BMS, but the problem remained (for 1 second Multiplus showed the SOC according to JK BMS but then changed back to 100%).
The JK inverter BMS has seen a lot of issues when in closed loop communication. The JK BMS saw a lot of hype and then a lot of disappointment. JK hasn’t done a lot to help the DIY community get past the issues.
Disconnect the communication cable and see how the system responds. I believe that the current firmware version for the BMS is 15.38.
I have the JK BMS and a Quattro 48/3000 running in open loop communication. It works fine in that configuration. Closed loop communication isn’t necessary.
You mean LuisVDW solution? I saw it yeah, but I managed to connect the BMS via CAN port, simply choosing in BMS setup in CAN option the Victron CAN protocol.
No, that was my first check, it was on automatic, but yesterday it worked fine. Anyway today I set it to JK BMS monitor instead of set, but that did not solve the problem, it was not charging the battery either. But when I chose „no battery monitor“, than it it passed some 1-3A to battery (it was visible on the Victron app, not the Venus).
Re DVCC I need to check. Yet the system died again. I asked a friend to charge up a smaller battery (Pylontech). I want to try tomorrow what the system will do with it.
This is how the VRM looks like. You can see the SOC is jumping from 95% to 63% (this is according to JK BMS) for a second and then back.
Both Multiplus and DVCC is set to JK BMS.
Moin, first change settings in the JK-BMS : the SOC-100% Volt to 3,450V and the cell OVPR to 3,449V and your charge/discharge temps are 20°C to high.
With your high 100% settings the BMS run into cell OVP when charging.
It controlled the old battery‘s main positive connection to the Multiplus. With the battery change from pylontech to new bigger box I let the battery to get charged with higher amps and the fuse blew. This caused the alarms.
After the New battery was fully changed and balanced, both the JK BMS and MultiPlus recalibrated itself and now show the correct SOC.