I need some help understanding the Victron ecosystem/options. Any advice, explanations, pointers to docs, or directions to pursue would be very appreciated.
I’m looking for a simple DC system for a small (20 ft) sailboat on a mooring in New Hampshire with Wi-Fi access to run a pump with notifications. No inverters, no alternators. The pump will be needed for rain.
I want monitoring/notifications because I have had bad experiences with pump/battery failures.
Thinking of a LiFEPO4 battery, MPPT 75/15, fixed 55W solar panel (for physical size reasons), smart shunt for SOC, and a Cerbo-GX. If the 55W panel isn’t enough, I could add another panel and wire it in series (the MPPT could handle V/A easily, and I could manually position a second one when leaving the boat) and/or occasionally charge on shore (especially if a Lithium lower-weight battery).
See the attached diagram for what I am thinking about.
-
Am I missing anything? Is the MPPT choice reasonable, or is another model better?
-
Do you have any LiFEPO4 model/brand recommendations? Victron seems very expensive with limited availability. Thinking of internal BMS for one less competent. 50Ah or 100Ah.
-
Optionally, I might use a second smart shunt in DC monitor mode to alert on any usage of a higher second pump, which should never activate absent a failure of the primary pump. Is there an easier way of getting such an alert? A smart shunt seems like overkill.
-
I am unclear about the importance of the MPPT load shutoff, given the presence of a BMS on the battery. Also, whether or not to wire the Cerbo-GX after the MPPT load or directly to the battery (after the SOC smart shunt)
Thank you for any advice.