Real-World Solar System Issue: The “Good” Fuse That Killed My System

I recently encountered a frustrating issue with my Victron-based solar system using lead-acid batteries. Everything seemed fine — until suddenly, nothing worked:

  • No charging from any source.
  • Inconsistent voltage readings.
  • Communication glitches.
  • Erratic behavior from inverters and charge controllers.

After hours of troubleshooting, double-checking settings, connections, and even suspecting firmware bugs, I found the unexpected culprit:

:backhand_index_pointing_right: A fuse that tested “OK” with a multimeter… but was actually the problem.


:light_bulb: The Root Cause

The fuse had partially melted internally. It still showed continuity with a voltmeter (low resistance), but under load it caused a significant voltage drop — enough to confuse the entire system.

In DC systems (especially low-voltage, high-current setups), this type of issue is dangerous:

  • The fuse doesn’t blow completely.
  • It limits current silently.
  • It causes voltage drop that leads to false logic and cascading faults in connected devices.

:magnifying_glass_tilted_left: Key Symptoms

  • Everything appears normal when idle.
  • Voltage drops drastically under load.
  • Devices stop charging batteries or shut down unexpectedly.
  • Logs and readings don’t make sense anymore.

:white_check_mark: Lessons Learned

  • Don’t trust continuity tests alone — especially in DC systems.
  • Always check voltage drop across fuses under real load.
  • If something doesn’t add up and the fuse is old or suspect: just replace it.
  • A “passing” fuse might still be a silent killer.

:wrench: Quick Tip for Victron Users

If your MultiPlus, BMV, or MPPTs are acting weird all at once and nothing charges…
Check your fuses. Even the “good” ones.

1 Like

@Pascal83
Appreciate the share. It will help many here.

There are many a system let down by resettable fuse/ breakers as well.

What fuses were you using on your system?

1 Like

Thanks, a very old one, don’t know how to describe. I replaced it with a MEGA Fuse from Victron. The origin of the issue came from a overload.

1 Like