Hello,
I recently finished my Solar System with 3 MP2 (one of them is a GX).
In the beginning I had 1 LUX-X48100LCG01 und 3 LUX-X48100LMG01.
They were interconnected with each other and then connected to the MP2GX via CAN.
The battery was/is detected as a Pylontech Battery.
I configured the ESS in accordance with the pdf from @Angie-Felicity.
Everything was working fine, I use a Shelly Pro3EM as a grid meter via Modbus TCP, grid point set to 0.
After one week of operation I decided to go max on the battery so I orderd 4 more LUX-X48100LMG01. Before connecting everything i made sure they all had roughtly the same SOC and were within 1 Volt of each other (Felicity guide sais 3 Volt but that seams a bit much for me).
Since i have this setup i get eratic/periodic discharge power bursts of 13 kW. So every MP2 feeds into the grid with max power. The SOC of the battery does not matter.
I thought maybe that was to balance the packs and cells but we had realy nice sunny weather for the last 4 days and the batteries were all at 100% SOC for 2-3 h per day. Is this enought to properly balance the packs and cells withhin?
I then changed the grid meter to the internal sensor of the MP2 because maybe I was getting wrong readings, but nothing changed, I still got max bursts of battery discharge.
These bursts only last 2-10s. I was unable to identify a pattern.
On the remote console i get lots of High cell voltage warnings, but according to other users this appearently is normal when you have a new system and the cells are getting balanced at high SOC.
I think the eratic bahavior has something to do with DVCC which is forced to “ON” via the Battery BMS.
I only started getting these discharge spikes after upgrading the battery to 8 packs.
Grid meter before the Upgrade:
Do you have any idea what is causing this?
Thank you,
Hichi